Dont overlook the fact that the Approved document B in some cases allows a single stair without lobbies up to 5 floors. I think the old FP act guides looked for lobbies if you went to three storeys and above.
It would be most unusual not to put detection in a stair if putting it in offices off the stair- it goes against the old philosophy of systems building up in coverage- M, L3, L2, L1.
It may not be wrong to do it- if the detection is purely in specific areas in lieu of lobby protection you could perhaps through a risk assessment justify it as an L5 system. For what it would save on the cost of the installation though- probably one or maybe 2 detectors I reckon it isnt worth it. Probably cost more thinking about the weasel words to put in the risk assessment and variation to BS5839