BS 5839 states that a smoke detector should be sited approx. 1.5m to the opening of any flue like structure, ie lift shafts.
What is the common accepted tolerance on the word approximatley, is 1.6 m ok?
BS 5839 Part 1 is a set of recommendations.
Variation from the recommendations is recognised and allowed.
The maximum area of coverage of an automatic fire detector is specifically mentioned as an example where the recommended values are considered to be arbitrary
However any Variation from the recommendations should be clearly identified at every stage; Design, Installation, Commissioning and Documentation.
All of the above can be found at BS5839 Part 1 2002 Clause 7
Also all Variations should be agreed by all Interested Parties (Clause 6)
If you can prove, or get someone to agree, that siting your detector within 1.6m instead of 1.5m from the opening of the flue-like structure, does not detrimentally affect the performance of the system then you have no problem. If not, move it and enjoy the 'peace of mind' afforded by the 'protection' of the recommendations of BS5839 Part 1!!!!!