Author Topic: Individual Fire Risk Assessments for Service Users in Nursing Care  (Read 18672 times)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Individual Fire Risk Assessments for Service Users in Nursing Care
« Reply #15 on: November 19, 2007, 12:28:39 PM »
Fully agree with you midland retty- sorry for any misunderstanding.  

In general within my experience of the care sector there are always generic hazards that are expected as the norm- chain smoking, substance use and abuse, careless disposal of smoking materials, these do not warrant more than a tick in the box on the individual care plan because they are expected and the fire risk assessment will refer to the benchmark risk control measures and systems for dealing with this.

In the case of clients with specific histories or needs for whom the benchmark is inappropriate  then either there will be a decision that the individual cannot be offered care or a review of the additonal risk control measures  needed to cater for that individual, within the individual  persons care plan. The outcome of this may then be an input into the fire risk assessment for the premises.

Midland Retty

  • Guest
Individual Fire Risk Assessments for Service Users in Nursing Care
« Reply #16 on: November 19, 2007, 12:49:15 PM »
No worries Kurnal I see where you are coming from with regard to the risk assessment of standard service user groups too.