Dave
Never mind waiting until the BCO completes his work you should be voicing your reservations to him now. Who undertook the statutory consultation for the FRS, did they pickup or perhaps miss something, check closely the specs on the plans.
When I was an IO with an FRS we had an excellent relationship with building control and worked at helping each other, once the BCO signs off the building it will be very difficult if not impossible to get things changed.
Get your thoughts into the BCO and the alarm installer so that they can see the errors before its too late and point out the correct clause of 5839
The letter is already in the post.
The project is through a partnership scheme so the orignal consult went to a BCO from another area whilst the inspection are being carried out by the local BCO. Unfortunately, we have a number of issues including this one all of which have been highlighted to all parties at various stages.
The next step is to examine the ceiling tiles to make sure they aren`t perforate but, I suspect that that would be obvious by looking.
With regards to it being difficult to get things changed, in most circumstances I would agree but, without detection in the corridor we aren`t satisfying the requirements for a dead end condition.
Thanks for the advice everyone.