Author Topic: Vesda sampling system  (Read 18964 times)

Offline asl

  • Newbie
  • *
  • Posts: 2
Vesda sampling system
« on: January 21, 2008, 11:48:35 AM »
Hello all.
Can anyone confirm whether a Vesda detection pipe can be extended by a couple of metres to detect an additional area without running a feed  back to the original panel please and would the panel have to be recalibrated?
Just general opinion please as we are getting different advice from different installers.

Many Thanks
asl

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Vesda sampling system
« Reply #1 on: January 21, 2008, 11:55:46 AM »
I am not technically competent so take this with a pinch of salt.
IMO a couple of metres should not make much difference to the flow levels in the pipe, my justification for saying this was that recently a sensor pipe was completely broken in half about 45m out from the panel and no faults or flow errors were detected by the panel (on an air sense technology quadra unit) .

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Vesda sampling system
« Reply #2 on: January 21, 2008, 01:06:58 PM »
If you want to protect an additionl area, then an additional run should be made. It will be a different address etc.

Offline asl

  • Newbie
  • *
  • Posts: 2
Vesda sampling system
« Reply #3 on: January 21, 2008, 02:00:00 PM »
Many thanks for the response guys.
Just to clarify we are fitting an additional comms cabinet in an existing computer room so its not truly another area.
Is this a "try it and see" situation or is there more technology involved? (we havent at this stage got a supplier seriously involved as we wanted to get a handle on it ourselves first.
Many thks for the advice

Regards

asl

Offline Thebeardedyorkshireman

  • Jr. Member
  • **
  • Posts: 96
Vesda sampling system
« Reply #4 on: January 21, 2008, 04:36:16 PM »
I looked at this one for a while before making a responce as the answer could range from very simple to very hard.
There are a number of VESDA products on the market but let us assume you have a lazer plus device and not a scanner. If the design of the vesda system protects the room with  seperate units and the cabinets with seperate units then adding a short length of pipe and another hole will increase the dilution and reduce the sensitivity. This can be compensated for in the settings and the sensitivity increased ( assume it is not on max now). Simple answer.

Vesda works by drawing air through a sampling chamber by an air pump ( fan) from the risk, via pipes. At commissioning the whole thing will be balanced by the engineer. I have seen people get the design  totaly wrong such that the pressure differential between the exhaust and the sample holes has defeated the pump and the air has flowed the wrong way thus rendering the whole thing useless. Thus the answer will be dependant on the static and dynamic pressures achieved inside the cabinet with the a/c running and off. You may invalidate the protection to the existing cabinets by making your proposed alteration. Hard answer!!! Why not get your problem looked at by somebody you can trust?

Beware of the many cowboys that are in our industry. Must dash now as I have to get a letter on the deadwood stage or butch and the boys will have no vesda pipe to throw in ( sorry install ) next week. More pills please matron and I didn't mention ASPIRE once HA!
Dave
Dave

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Vesda sampling system
« Reply #5 on: January 21, 2008, 05:42:53 PM »
Quote from: asl
Many thanks for the response guys.
Just to clarify we are fitting an additional comms cabinet in an existing computer room so its not truly another area.
Is this a "try it and see" situation or is there more technology involved? (we havent at this stage got a supplier seriously involved as we wanted to get a handle on it ourselves first.
Many thks for the advice

Regards

asl
I'm confused.... you will either have primary detection, or secondary or both. That is, you will have vesda pipework installed in front of the return air grilles thereby sampling air from the entire room and therefore no need to extend pipework. Or you will have pipework installed at ceiling level or in a void (possibly above the ceiling and in a floor void) and again you will be sampling air from the room - spacings determined by BS6266 etc therefore no need to extend because you are installing a cabinet.

The only other option is that you have specific in cabinet detection. In which case extending a pipe a couple of metres and adding a sampling hole will make very little difference.

However, you should get a competent company to check out the existing design and run it through the design software supplied by the system manufacturer in order to verify the flow, balance and sensitivity and basically re-commission the system.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Vesda sampling system
« Reply #6 on: January 21, 2008, 07:27:42 PM »
Dave,
what are you aspiring to?

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Vesda sampling system
« Reply #7 on: January 21, 2008, 10:13:03 PM »
Quote from: jokar
Dave,
what are you aspiring to?
Oh dear.... someone fetch Jokars funny file.......... yes thats it.... the very thin one.......!!!!

:D
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Steve_gb

  • Newbie
  • *
  • Posts: 16
Vesda sampling system
« Reply #8 on: February 03, 2008, 07:09:03 PM »
50 metres is the max length..if ur happy to keep the room on one zone then no harm done!
Steve McCarley

steve_gb@hotmail.com

Offline Gazzaaa

  • Newbie
  • *
  • Posts: 4
Vesda sampling system
« Reply #9 on: February 06, 2008, 03:48:25 PM »
Well done Steve_gb you nearly remembered. To extend the pipework of a VESDA detector you should use the ASPIRE software program to ensure that the detector will work to the required sensitivity and timings. Thats the correct and responsible way of doing it.

Here's some rules of thumb though. A VESDA LaserPLUS (VLP) has four pipes but does not distinguish between which pipe detects the smoke. Each pipe could cover the return air grilles, known as primary detection, the room space or voids, known as secondary detection or be installed with a sampling point into each cabinet, known as cabinet protection.

If all four pipes are used, each pipe can be a maximum of 50m in length. If only two pipes are used each pipe could be 100m in length. For room detection hole spacing should be 5m apart (BS6266) or 10m apart (BS5839).

To answer the question above, assuming that the addition of an extra cabinet means that it is cabinet protection that is being implemented, as long as the pipework is under 50m in length and any capillaries used are under 2m in length, and as long as there are no more than 10 holes in a 50m length of pipe you will probably find that adding one aditional hole will not create any problems.

If it does create a problem it will probably be that it affects the flow rate which will more than likely only reduce transport time from the end hole. This could be corrected by increasing the fan speed of the detector. Sensitivity can also be easily adjusted to take account of the extra hole (although i suspect this would not be required)

You may also find that if the transport time is increased it is still within parameters. BS allows for a max of 120 secs for the transport time. Xtralis, the manufacturers of VESDA, recommend 60 secs. You will probably find that the origional calcs were done to meet this 60 sec target and therefore an additional hole wouldn't make much difference.

Or you may find, as suggested above, that it was done by cowboys in which case none of the above applies and you should just add your extra hole anyway.

Offline Steve_gb

  • Newbie
  • *
  • Posts: 16
Vesda sampling system
« Reply #10 on: February 06, 2008, 07:08:54 PM »
is this the Yorkshire Gaazzzaa?
Steve McCarley

steve_gb@hotmail.com

Offline Kevin Shea

  • Newbie
  • *
  • Posts: 15
    • http://www.xtralis.com
Vesda sampling system
« Reply #11 on: February 08, 2008, 09:15:38 AM »
Hi asl,

The advice Gazzaaa has given you is very good. I work for Xtralis (the chaps behind the VESDA fire deteciton) and I will happily get in touch with you to provide any help or advice on any VESDA projects you have any niggles with. With regards to flow rate yes, while BS does allow for a max transport time of 120 seconds we as the manufacturer do suggest a shorter time 60 seconds. This all can be easily calculated from the ASPIRE pipe design program you can download and use for free at:

http://www.xtralis.com/opencms/opencms/system/modules/com.vfsportal/default_bodies/apac/int_en/products_fire_softwaredownload_aspire2.html

Sorry about the long web address! Either way take a look and see what you think, a lot of installers and fire system designers have found it useful when specing or installing the VESDA systems. Either way, any problems give me a call and I'll gladly speak with you!

Kevin Shea
KShea@xtralis.com
01442 206 429

Offline Ken Taylor

  • Sr. Member
  • ****
  • Posts: 414
Vesda sampling system
« Reply #12 on: February 08, 2008, 06:24:10 PM »
Do you still get unwanted alarms with these when someone decides to engage in a rather dusty activity within the room, Kev? My recollection is of building management having to switch off the system from time to time and then remembering to put it back on again -  I ask in as much as extending a pipe to another room could have implications for fire detection in another should the system be switched off - so management would need to plan for this.

Offline Gazzaaa

  • Newbie
  • *
  • Posts: 4
Vesda sampling system
« Reply #13 on: February 11, 2008, 03:35:58 PM »
Ey Up Steve_gb - Does that answer your question?

Ken, the Vesda detector you probably remember is the old style E70D. These detectors were designed for extremely sensitive early smoke detection and used a Xenon type strobe to detect the smoke particles.

The type that are around now are laser based and incorporate a dual stage filter that filters pretty much everything except smoke sized particles from entering the laser detection chamber. Unlike the old Xenon based product, the sensitivity is adjustable from around 0.005% to 20% obscuration per meter. Typically a standard smoke detector has a threshold of around 4% obscuration per meter. As you can see, you can make the Vesda detector extremely sensitive or a lot less sensitive than a standard point detector.

I do know of issues where the detector struggles in certain circumstances though, such as cement works. It would seem that powdered cement has the same particle size as smoke. On the other hand, i have seen false alarm testing carried out in an underground carpark with a Vesda detector installed. The test consisted of the oldest, most delapidated, Transit van being fired up and revved up to kick as much diesel fumes and smoke as it could into the underground car park. The Vesda detector did not go into alarm condition. After all the smoke & fumes cleared, a smoke pellet was lit which pretty much instantly triggered the detector.

Offline Ken Taylor

  • Sr. Member
  • ****
  • Posts: 414
Vesda sampling system
« Reply #14 on: February 11, 2008, 07:54:29 PM »
Thanks, Gaz. I've had this sort of issue with large rooms in historic listed buildings during maintenance works and the like.