Author Topic: earth fault Menvier Mf400 panel  (Read 8445 times)

Offline John@EPL

  • Newbie
  • *
  • Posts: 27
earth fault Menvier Mf400 panel
« on: January 22, 2008, 10:59:21 PM »
Hi all.
I have been trying to fault find an earth fault that has occurred on a alarm system I look after. The panel is a menvier MV400. It isn't that old and is a quality install.
It has just started to show an earth fault flashing light and beeping on the panel. Nothing has happened in the property to alter the wiring or detectors, no leaks etc. Everything looks fine. Don't really want to strip it down to do an insulation resistance test as I refuse to believe a cable has just broken down. Therfore I can only assume there is another culprit.  In any ones experience what else can cause the same fault? Detector failure? board fault? back up battery is 3.4Ah which is down on the 4Ah required .... sometimes that can throw a wobbly on some cts  but earth fault??

Any ideas anyone?

Thanks

John

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
earth fault Menvier Mf400 panel
« Reply #1 on: January 23, 2008, 08:54:58 AM »
The earth fault detection circuitry, on most panels, requires the mains supply earth to be connected for the monitoring to work. An engineer can temporarily disconnect it for fault-finding purposes. If the earth fault remains when the mains supply earth is disconnected, then there is a higher liklihood that the fault is with the panel monitoring circuit rather than on the outgoing circuits.

However the fault is more likely to be on an outgoing circuits. Water leaks into equipment or someone banging a nail or screwing a screw into a cable somewhere are common causes for sudden earth fault indication.

The first stage of outgoing circuit fault-finding is to remove the earths from outgoing circuits one at a time (until the faulty circuit is detected by the fault warning going away) to find the affected circuit. From there it is a matter of using a resistance measuring meter and breaking down the circuit(s) until the earth fault is located.

Offline John@EPL

  • Newbie
  • *
  • Posts: 27
earth fault Menvier Mf400 panel
« Reply #2 on: January 23, 2008, 05:29:29 PM »
I was thinking along the same lines when I looked at it first. The fault disappears when the supply earth is disconnected. So I guess the panel is ok. However I disconnected all of the zone and bell circuit earths and I was still getting a fault (with the supply earth connected). Which got me thinking about other circuitry wobblies connected to  such things as low back up batteries. Not experienced it myself but have read reports that these things can cause wobblies. Wouldn't have thought so myself tho.
I don't think anything has occurred to third party cause the problem. I visually saw all detectors, no damp patches, no leaks at all. All cabling looks tidy and concealed in a central duct up the center of the house. The last thing is the fault occurred in the middle of the night when everyone was in bed? Apparently there was an earth fault problem previously a few years ago and another service co solved it but nothing is written in the log book to say what they did.

Thanks for your help

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
earth fault Menvier Mf400 panel
« Reply #3 on: January 23, 2008, 06:20:02 PM »
My advice would be after you have checked all cabling including supply is to power down start up again with new battery and then introduce the cables one at a time if the fault is still there after power up then change panel.Had this problem with a morley addressable system that had a earth fault removed the problem but still the earth fault stayed on the panel.
Hope this helps.

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
earth fault Menvier Mf400 panel
« Reply #4 on: January 23, 2008, 06:24:55 PM »
Also i had this problem before and the problem was the earth was touch the negative slightly and all the earths were screwed to the back boxes and then it was sort off speak earthed to the main building.Check to see if you have continuty on any of your cables i;e earth to pos or neg.This could be your problem

Offline John Dragon

  • Full Member
  • ***
  • Posts: 189
earth fault Menvier Mf400 panel
« Reply #5 on: January 23, 2008, 08:40:46 PM »
I have had a similar prob on a few addressables, power down and restart cured it in each instance.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
earth fault Menvier Mf400 panel
« Reply #6 on: January 23, 2008, 10:15:46 PM »
We had one with an old ZXe of Morley, when disconnected all wires from the panel the earth fault did not disappear it was certainly in the PCB... (The system was old enough to be brought to the mortuary and get it ready to be buried...)

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
earth fault Menvier Mf400 panel
« Reply #7 on: January 24, 2008, 08:46:21 AM »
But this not a blame to Morley systems!