Author Topic: Fire Alarm Testing in Flats  (Read 3383 times)

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Fire Alarm Testing in Flats
« on: February 04, 2008, 07:30:49 PM »
How do you get round the testing of fire alarms in flats where no resident wants the responsibilty, and the managing agent simply is not around to do it. It is only a manual system and has the quarterly inspections carried out by a fire alarm engineer.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Fire Alarm Testing in Flats
« Reply #1 on: February 04, 2008, 08:18:01 PM »
If the building complies with ADB or 5588 part 1 or CP3 take the manual common areas alarm out.

If it doesn't comply with these codes it needs detection in the common areas. Then arrange a maintenance and testing contract with a local company. If it needs a manual areas alarm system the risk of vandalism is too great to leave it 3 months between checks, connect the system to a monitoring centre and initiate fault monitoring so that will cover the daily inspection of the panel