We have recently discovered that Securiton system which is a German analogue old system with a radial sounder circuit, this later is linked to the panel through a Relay (C, NO), each time we test the system with maintenance mode, every thing was working OK, last week one of the mental patient broken the glass in level 6 fire exits and run away, just after servicing and enabling the out put back to normal, alarm when off for few seconds and stopped, then an earth fault appeared.
The strange thing is that the earth fault come up only when testing alarms live, in maintenance mode it would not, that's what we have found any way.
We used to service the system in silent mode as no alarm was allowed on site the time we test it.
Would this kind of system, still acceptable by BS5839 nowadays, or should it be entirely changed by a BS5839 well complaint system?
Thank you