Dead End Travel
« on: February 12, 2008, 10:38:39 AM »
In the typical scenario where you have dead end corridor with offices off the corridor, if the travel distance can be met by the furthest office to a final or storey exit, is there still a need to have smoke detection or make the corridor FR?
"We are the unwilling,
Led by the unqualified,
Doing the unnecessary,
For the ungrateful.
-Living the dream!"

Offline FSO

  • Full Member
  • ***
  • Posts: 216
Dead End Travel
« Reply #1 on: February 12, 2008, 01:07:54 PM »
Yes you will either have to protect the corridor of install AFD in this situation.

If a fire was in an office near to the exit, it would comprimise the exit for other room users.

Jay