Author Topic: Testing Detectors On Old Systems  (Read 16639 times)

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
Testing Detectors On Old Systems
« on: March 17, 2008, 07:41:34 PM »
The Company I Work For Just Got A Contract With Alot Of Old Fire Alarms On Big Buildings.there Is No One Man Walk Test Or Any Other Functions Apart From The Basics. So My Question Is,is It Alright To Test More Than One Detector On The Same Zone Then Reset The Panel.the Biggest Building Has Twelve Floors With A Seperate Zone On Each Level Which Is Good But Not When It Comes To Testing It. No Elevator In This Place Just Alot Of Steps. I Normanally Test One Detector In Each Zone Then Go Back To The Panel To See If The Zone Light Comes Up Then Reset It.but It Would Be Handy If It Is Alright To Test A Floor At A Time. 50% Service Every 6 Months. Approx 20-25 Detectors In Each Zone.

Offline John Dragon

  • Full Member
  • ***
  • Posts: 189
Testing Detectors On Old Systems
« Reply #1 on: March 17, 2008, 08:10:02 PM »
http://www.firesense.co.uk/miscella.htm

Maybe this gadget will help?

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
Testing Detectors On Old Systems
« Reply #2 on: March 17, 2008, 09:14:49 PM »
Hey very good. Does anybody have one of these and are they any good.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Testing Detectors On Old Systems
« Reply #3 on: March 17, 2008, 09:18:11 PM »
Quote from: Davro
The Company I Work For Just Got A Contract With Alot Of Old Fire Alarms On Big Buildings.there Is No One Man Walk Test Or Any Other Functions Apart From The Basics. So My Question Is,is It Alright To Test More Than One Detector On The Same Zone Then Reset The Panel.the Biggest Building Has Twelve Floors With A Seperate Zone On Each Level Which Is Good But Not When It Comes To Testing It. No Elevator In This Place Just Alot Of Steps. I Normanally Test One Detector In Each Zone Then Go Back To The Panel To See If The Zone Light Comes Up Then Reset It.but It Would Be Handy If It Is Alright To Test A Floor At A Time. 50% Service Every 6 Months. Approx 20-25 Detectors In Each Zone.
My first enquiry is how long did you take to start every single word with capital letter

My second enquiry is what make you are talking about?

Thirdly If the system is not two wire system why not just remove the fuses of the outputs (sounders, relays) when testing...

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Testing Detectors On Old Systems
« Reply #4 on: March 17, 2008, 11:50:13 PM »
Quote from: John Dragon
http://www.firesense.co.uk/miscella.htm

Maybe this gadget will help?
Lookis like a good idea but some panels don't like starting up on batteries.

Graeme

  • Guest
Testing Detectors On Old Systems
« Reply #5 on: March 18, 2008, 12:43:06 PM »
Quote from: Benzerari
Quote from: Davro
The Company I Work For Just Got A Contract With Alot Of Old Fire Alarms On Big Buildings.there Is No One Man Walk Test Or Any Other Functions Apart From The Basics. So My Question Is,is It Alright To Test More Than One Detector On The Same Zone Then Reset The Panel.the Biggest Building Has Twelve Floors With A Seperate Zone On Each Level Which Is Good But Not When It Comes To Testing It. No Elevator In This Place Just Alot Of Steps. I Normanally Test One Detector In Each Zone Then Go Back To The Panel To See If The Zone Light Comes Up Then Reset It.but It Would Be Handy If It Is Alright To Test A Floor At A Time. 50% Service Every 6 Months. Approx 20-25 Detectors In Each Zone.
My first enquiry is how long did you take to start every single word with capital letter

My second enquiry is what make you are talking about?

Thirdly If the system is not two wire system why not just remove the fuses of the outputs (sounders, relays) when testing...
that won't reset the system after a device is tested Benzerai

The Firesense unit is okay but ihave found that some panels don't take kindly to it,so i use an apprentice instead to push the reset button.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Testing Detectors On Old Systems
« Reply #6 on: March 18, 2008, 12:55:19 PM »
Quote from: Davro
The Company I Work For Just Got A Contract With Alot Of Old Fire Alarms On Big Buildings.there Is No One Man Walk Test Or Any Other Functions Apart From The Basics. So My Question Is,is It Alright To Test More Than One Detector On The Same Zone Then Reset The Panel.the Biggest Building Has Twelve Floors With A Seperate Zone On Each Level Which Is Good But Not When It Comes To Testing It. No Elevator In This Place Just Alot Of Steps. I Normanally Test One Detector In Each Zone Then Go Back To The Panel To See If The Zone Light Comes Up Then Reset It.but It Would Be Handy If It Is Alright To Test A Floor At A Time. 50% Service Every 6 Months. Approx 20-25 Detectors In Each Zone.
Since a full test infers that the operation of a detector includes that it indicates on the correct zone on the control panel you have two problems (on non-addressable systems) when testing more than one detector on a zone before reset. 1) Have the subsequent detectors properly operated the control panel that was already operated from the previous detector? 2) If you test a number of detectors in one fire zone and then return to the control panel to find a number of different zone indicators illuminated, how do you know which detector operated which zone?
The best panels are those that have a one-man test facility that pulse the fire bells as a code for which zone has operated (i.e once for zone 1 , twice for zone 2 etc) and then automatically resets.
Please note however that, my reading of the recommendations of BS5839 part 1 2002 is that you don't need to check that each detector indicates on the correct zone as part of the routine maintenance schedule or even that it signals the control panel at all! I would guess that it is presumed that the detector to panel operation and the zone allocation has been tested at commissioning or subsequent system modification and it is not going to change by itself since those times.
I'm sure that many on FireNet wouldn't agree that a simple detector operation test  is a sufficient test, but that's what BS intimates!

Chris Houston

  • Guest
Testing Detectors On Old Systems
« Reply #7 on: March 18, 2008, 12:58:06 PM »
Davro,

Did you actually put a capital letter on every single word, or did the FireNet software do this?  Did you perhaps put everything in capitol letters (which I think our software will not allow).

Either way, it makes for difficult reading, if you could put future posts in the normal format, I am sure we would all be very grateful.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Testing Detectors On Old Systems
« Reply #8 on: March 18, 2008, 02:08:40 PM »
Quote from: Graeme
Quote from: Benzerari
Quote from: Davro
The Company I Work For Just Got A Contract With Alot Of Old Fire Alarms On Big Buildings.there Is No One Man Walk Test Or Any Other Functions Apart From The Basics. So My Question Is,is It Alright To Test More Than One Detector On The Same Zone Then Reset The Panel.the Biggest Building Has Twelve Floors With A Seperate Zone On Each Level Which Is Good But Not When It Comes To Testing It. No Elevator In This Place Just Alot Of Steps. I Normanally Test One Detector In Each Zone Then Go Back To The Panel To See If The Zone Light Comes Up Then Reset It.but It Would Be Handy If It Is Alright To Test A Floor At A Time. 50% Service Every 6 Months. Approx 20-25 Detectors In Each Zone.
My first enquiry is how long did you take to start every single word with capital letter

My second enquiry is what make you are talking about?

Thirdly If the system is not two wire system why not just remove the fuses of the outputs (sounders, relays) when testing...
that won't reset the system after a device is tested Benzerai .
I agree, but what else can be done if the system has not got OMT option as stated in the original post, the only thing is that the system may need reset every 4-5 tests...

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
Testing Detectors On Old Systems
« Reply #9 on: March 18, 2008, 07:47:44 PM »
Sorry about the capitals, but i know that a mate of mine use to service this system (firedex 9000) and that he works with a big company who can afford two men on the job. I work as a part of a 3 man team and the boss always say's yes you can have 2 people then when the time comes the other man is booked in somewhere else,and yes i test 1 detector at a time then reset again,all i wanted to know is it o.k to put 2 or more detectors in fire on the same zone then reset it and does this make this service o.k.

Graeme

  • Guest
Testing Detectors On Old Systems
« Reply #10 on: March 18, 2008, 08:07:26 PM »
I would say no as with testing one at a time with OMT you can see if the panel has activated then reset by watching the LED.
By testing two then resetting you cannot tell if both would have activated the panel individually. Most cases when the led comes on it would have but i would be happier doing them one at a time to be sure.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Testing Detectors On Old Systems
« Reply #11 on: March 18, 2008, 09:30:23 PM »
Quote from: Graeme
I would say no as with testing one at a time with OMT you can see if the panel has activated then reset by watching the LED.
By testing two then resetting you cannot tell if both would have activated the panel individually. Most cases when the led comes on it would have but i would be happier doing them one at a time to be sure.
If they were accessible you could pop the heads out to reset them,although this can have it's downside - if you don't put one back into the base correctly you end up chasing a fault.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Testing Detectors On Old Systems
« Reply #12 on: March 19, 2008, 08:42:55 AM »
Quote from: Buzzard905
Quote from: Graeme
I would say no as with testing one at a time with OMT you can see if the panel has activated then reset by watching the LED.
By testing two then resetting you cannot tell if both would have activated the panel individually. Most cases when the led comes on it would have but i would be happier doing them one at a time to be sure.
If they were accessible you could pop the heads out to reset them,although this can have it's downside - if you don't put one back into the base correctly you end up chasing a fault.
But this doesn't reset the panel! - Which is the element that takes time to walk back to the panel and reset.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Testing Detectors On Old Systems
« Reply #13 on: March 19, 2008, 08:44:54 AM »
Quote from: Davro
Sorry about the capitals, but i know that a mate of mine use to service this system (firedex 9000) and that he works with a big company who can afford two men on the job. I work as a part of a 3 man team and the boss always say's yes you can have 2 people then when the time comes the other man is booked in somewhere else,and yes i test 1 detector at a time then reset again,all i wanted to know is it o.k to put 2 or more detectors in fire on the same zone then reset it and does this make this service o.k.
Did you read my earlier post?

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Testing Detectors On Old Systems
« Reply #14 on: March 19, 2008, 08:50:42 AM »
Quote from: Graeme
I would say no as with testing one at a time with OMT you can see if the panel has activated then reset by watching the LED.
By testing two then resetting you cannot tell if both would have activated the panel individually. Most cases when the led comes on it would have but i would be happier doing them one at a time to be sure.
Graeme, I accept your point but I would argue that BS doesn't appear to insist on this. Also technically most panels will handle a number of detectors operated at the same time on one zone. Therefore it is technically possible and BS doesn't recommend otherwise. Therefore surely the simple answer to Davro is 'yes, you can do it this way!'.