BAFE Inspection and 5839 pt1 2008 ???
« Reply #15 on: September 26, 2008, 10:33:41 AM »
Quote from: David Rooney
Quote from: Chris Houston
OK, must admit now I'm a bit confused, thought the boiler room was attached but separated by a concrete wall.  If it is detached and some distance away, then I will reconsider my points.  If it is attached, then an evacuation must surely be undertaken.
I'd think of the boiler room as a semi detached bunker.

I suppose the evacuation should be undertaken - after all if the detector in their went off it would evacuate the lot......

It just seems overkill to install the call point when as you say the guy could run off and find another one......
And there is a detector in the boiler room.
We're not Brazil we're Northern Ireland.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
BAFE Inspection and 5839 pt1 2008 ???
« Reply #16 on: September 26, 2008, 12:19:08 PM »
No one should ever have to exit a part of the building and then re-enter another part just to operate a call point.

Many boiler houses these days are integral to a building, but with access only from external to the rest of the building and I would assume that the fire resistance from the boiler house to the rest of the building is very high.

However, whilst it might seem unlikely that the person in a smallish boiler room wouldn't be able to exit quite quickly in an emergency, the need to be able to raise a fire alarm warning signal is surely important. It is likely that a fire in a boiler house could quickly become a serious problem, due to the close proximity of fuel etc., and I see the need to quickly warn others to evacuate the rest of the building in the event of a fire in the bolier house as important.

For my part, I consider these sort of boiler houses need the relevant automatic detection and at least one manual call point (all allocated on their own fire zone if the boiler house can only be accessed external to the main building) and at least one audible and one visual warning device (because boiler houses can be noisy).

Chris Houston

  • Guest
BAFE Inspection and 5839 pt1 2008 ???
« Reply #17 on: September 26, 2008, 03:48:03 PM »
If it is attached, even if separated by a concrete wall, then you must evacuate.  The concrete wall may have penetrations, the roof might ignite and burn over, too many unknowns.

I think BAFE were right, but accept it is pretty far down the list of priorities and most boiler rooms probably don't have them.  If that was all they found wrong, I think you are doing a good job!

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
BAFE Inspection and 5839 pt1 2008 ???
« Reply #18 on: September 26, 2008, 04:57:08 PM »
Quote from: Chris Houston
I think BAFE were right, but accept it is pretty far down the list of priorities and most boiler rooms probably don't have them.  If that was all they found wrong, I think you are doing a good job!
Oh stop it... I'll blush.....
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic