Author Topic: Fire Strategies  (Read 4114 times)

Offline MC

  • Newbie
  • *
  • Posts: 18
Fire Strategies
« on: May 06, 2008, 11:56:21 AM »
Hello
Can anyone give me some advice where to look up information, documents, examples etc of Fire Strategies for properties new and old. I am not 100% up to date with this subject and wish to learn more. I have PAS 911 but have not seen a documented Fire Stategie yet.

Kind Regards

MC

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Fire Strategies
« Reply #1 on: May 06, 2008, 12:08:10 PM »
Is this a fire strategy to support an application for Building Regulations approval or a fire emergency plan?

Offline MC

  • Newbie
  • *
  • Posts: 18
Fire Strategies
« Reply #2 on: May 06, 2008, 01:55:46 PM »
Building regs approval

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Fire Strategies
« Reply #3 on: May 06, 2008, 02:53:17 PM »
Is the building likely to be broadly compliant with ADB  or will fire engineering be required?
The reason I ask is because its horses for courses- for a building that is broadly compliant the strategy document just  supports the H&S file produced for the CDM  and Building Regulation 16B so runs through the functional requirements B1 - B5  summarising how the requirements are met   but if  a fire engineered solution is required then much greater detail is required justifying the proposed solution.