Can I have your thoughts please on this re-occurring problem.
A fire alarm system is to be linked to an intruder alarm system STU for monitoring. I know this gives a whole load of issues in terms of battery standby etc but putting those aside having overcome them as far as reasonably practicable my question is this:
The fire panel in question has fire & fault contacts but these are not monitored for cabling faults between the panel and the STU.
The fire contact can be overcome by using a spare sounder circuit to fire a relay at the STU and therefore monitor the cable by using the EOL resistor for the sounder circuit.
How can the fault contact cabling between the panel and the stu be monitored?......and I can't use an interface on the loop because these can't be programmed to mimic a fault on the fire panel.
Your help would be much appreciated.
Hi g4vjc, after the 'rushed' info I previously gave you I felt guilty and that I had to come up with something better, so I have been giving this a bit of thought.
I have an idea, but I haven't had time to precisely check out exactly what is available. However, maybe you can look into it.
Your idea to use a relay at the end of a monitored sounder circuit to use for the 'fire' signal may be possible to extend for your use with the 'fault' signal.
C-tec manufatcure a part FF502P which is described as a
'Four zone monitored sounder extender, supplied on a double gang plate. provides four extra sounder circuits with open and closed circuit fault monitoring, two trigger inputs and one fault output'I'm guessing that if you give the FF502P a 24V dc supply and connect your panel fault output relay to one of the inputs, and the your panel fire relay to the other input, then you will have two monitored circuits that will operate to 'fault' and the other two to 'fire'. The fault output of the FF502P could be interfaced in some way to generate a fault on the fire panel indicating open or short circuit on one of the links between the cie and the enclosure housing the transmission device as required by BS.
As I previously said, I haven't had time to check out this C-tec part - but it sounds like it could work. If not, maybe someone else supplies this type of monitoring pcb that would operate as I have described above.