Hi M11.
I love innocent questions that open up huge grey areas in our industry. And you have just opened up a massive one.
This could get long and complicated when I start quoting statutes, so I will try and keep things simple.
If you follow from top to bottom (hopefully) you will see why some companies follow the practice of renewing the horn at test.
1. CO2 extinguishers and their associated parts, fall under the Directive 97/23/EC ( PED - Pressure Equipment Directive) And have category III classification.
http://ec.europa.eu/enterprise/pressure_equipment/ped/guidelines/guideline1-1_en.htmlhttp://ec.europa.eu/enterprise/pressure_equipment/ped/guidelines/guideline2-14_en.html2. And as such, in the UK they also fall under:
Statutory Instrument 2004 No. 568 (The Carriage of Dangerous Goods and Use of Transportable Pressure Equipment Regulations 2004)
Statutory Instrument 1999 No. 2001 (The Pressure Equipment Regulations 1999)
Statutory Instrument 2000 No. 128 (The Pressure Systems Safety Regulations 2000)
3. The above are enforcable by law.
Penalties
26. - (1) A person guilty of an offence under regulation 25(a) shall be liable on summary conviction -
(a) to imprisonment for a term not exceeding 3 months; or
(b) to a fine not exceeding level 5 on the standard scale,4. 97/23/EC uses two general terms "The Vessel" basically the cylinder and "The Assembly" basically the bits that go to make up the pressure vessel i.e. cylinder, valves, discharge lines, or anything that will be pressurised during discharge or hold pressure during containment.
QUOTE ANNEX 1:
" The obligations arising from the essential requirements listed in this Annex for pressure equipment also apply to assemblies where the corresponding hazard exists".5. The legal maximum period for pressure test of a category III pressure vessel (and this is the best bit) and / or pressure assembly is 10 years.
Because of that last requirement and because no pressure test apparatus for valves, horns and hoses has ever been purchased by any acredited UK test centre (probably because it's a throw away world too). Both valve, dip tube and discharge hose should be disgarded at time of cylinder pressure test.
The area that could be argued - but why bother as a CO2 horn costs peanuts - is that the discharge device is not fully pressurised during discharge but only handles outlet flow at a fraction of the cylinder / valve pressure and therefore should be exempt.
However, I don't think anyone would ever actually be that sad and bothered to run pressure flow tests on second hand kit against something that costs 2 quid to buy in new. The new horn will have to be CE compliant. lt will (should) have been tested at manufacture. Either way that's the manufacturers problem should there be trouble.
Personally, I use the John Dragon method and discount new kit down to PT/R level. I may make less coin but at least then I've got an extinguisher that has a BS/EN3 fire rating and is CE compliant. Which of course a PT/R (pressure test / refurb) has neither.