I have a client who manages a small 4 bed residential care respite facility for young persons.
The staff are persistantly propping open fire doors to the only corridor one being to a domestic size kitchen. The client would prefer to have an open door policy anyway thus providing a more homely less establishment type environment for the children.
We have discussed the provision of hold open devices to rooms containg smoke detection but have the usual problem with a HOD on the kitchen/dining door.
The kitchen contains a heat detector which I don't consider suitable for a HOD. Is there a suitable type of smoke detector which may suit a HOD on the kitchen door. The kitchen is domestic size with no deep fay frying. Contains toaster and dishwasher. Cooker provided with extraction hood.
Rather than try to resolve by increasing the level of extraction we would prefer a technological solution involving the AFD.
Any ideas from you techno-types out there?
Nearlythere, I don't know of any automatic detector that will give you any faster warning than the heat detector that is installed apart, of course, from a smoke detector. All the smoke detectors I am aware of will operate to one or the other effect caused by the cooking/washing in this area.
You obviously also understand that any open door policy is possibly going to give you problems with other smoke detectors installed elswhere in the area.
Could a solution be to leave the existing fire alarm system as it is and then add (but not to the existing system) a further smoke detector in the kitchen solely to release the hold open device? This will possibly give the option of closing the kitchen door quickly in the event of too much normal kitchen-use smoke-like effects, thereby possibly preventing some unwanted alarms, but with all the original fire detection elements still in place.
If this is a solution that you might consider, I can direct you to a gadget that provides power to the door holder and is provided with a monitored connection for a 'proper' smoke detector (that will disconnect the power to the door hold on fire operation) and it costs less than 40 squid. This would give you a possible standalone solution.
I apologise, to those that complain, if my post is long-winded, but I initially tried writing it and missing out every other word, but it made even less sense than it does now.