Author Topic: Yet another Morley problem  (Read 24835 times)

Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Yet another Morley problem
« on: July 24, 2008, 08:42:56 PM »
Will be attending this site tomorrow.

From what I remember, it is a 5 looper.

Basically, they have been having extremely erratic fire alarms from completely different locations over the last 2 days. A fellow engineer was on site today and checked every detector for the cause, No led activation from the device? Anyone any idea what this could be??

Overloaded loop? One device bringing the rest of the loop down??

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Yet another Morley problem
« Reply #1 on: July 24, 2008, 10:05:30 PM »
Quote from: JonnyG
Will be attending this site tomorrow.

From what I remember, it is a 5 looper.

Basically, they have been having extremely erratic fire alarms from completely different locations over the last 2 days. A fellow engineer was on site today and checked every detector for the cause, No led activation from the device? Anyone any idea what this could be??

Overloaded loop? One device bringing the rest of the loop down??
I do not think loop over loaded will set alarm off from different locations:

What did event log shows?

Has the system had any conventional sounders linked through sounder controller?

Also check the settings of the loop powered sounders they may have been set by mistake, to sound in fault condition instead of fire condition, I used to see such problems...

The worst of the worst scenario is to re-commission the system from the beginning and see what is going wrong.

Alarm going off with no zone LED illuminated could be through an evacuation button or input class change.

Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Yet another Morley problem
« Reply #2 on: July 25, 2008, 09:42:08 AM »
Maybe should have explained better. The panel shows a device in fire condition. Lets say L1 A13. But when he checked that device, There was no led lit on the device.

Yesterday in total he had 6 fire conditions from different locations with no cause and no led lit.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Yet another Morley problem
« Reply #3 on: July 25, 2008, 06:02:19 PM »
Johnny ,

The led gets the bit instruction from the panel to turn on , so in that case either you are at the wrong head or the led has failed.
I would view each device that is suspect and press key 2 which will turn on the led to confirm you are at the right device , or use a test set , Apollo hochiki , don't know what you are working on ?

It sounds more like corruption to me so access panel in commission mode , enter setup bring up the log section press change key and alter to diagnostic mode , put panel back to normal and leave it half an hour , when you view the log it will then give you indication with any devices that are playing up. However don't forget to put the log back to normal status from diagnostics.
Its time to make a counter attack !

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Yet another Morley problem
« Reply #4 on: July 26, 2008, 03:41:04 PM »
I have a site with ZX5e's and if I disconnect one of the loops (by removing the plug) I get sporadic fires up from devices on other loops.This happens on different panels and they were all installed in 2007.
Bundle of (IMO) junk these days.

Offline Buggy

  • Newbie
  • *
  • Posts: 18
Yet another Morley problem
« Reply #5 on: July 26, 2008, 04:44:50 PM »
Have seen this happen myself Buzzard (it isnt an airport your referring too?!), wouldnt blame the panel though. From my experience it is always problems in the field (dodgy cabling) or lack of continuity/poor bonding of the shield wire.



Good advice from Galeon

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Yet another Morley problem
« Reply #6 on: July 26, 2008, 08:11:17 PM »
Quote from: Buggy
Have seen this happen myself Buzzard (it isnt an airport your referring too?!), wouldnt blame the panel though. From my experience it is always problems in the field (dodgy cabling) or lack of continuity/poor bonding of the shield wire.



Good advice from Galeon
Yes old wiring with new panel could set such weired things, I used to see as well alarm goes off with any sort of fault condition, programming issue in a loop powered sounders !!!

Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Yet another Morley problem
« Reply #7 on: July 27, 2008, 10:34:43 PM »
Quote from: Galeon
Johnny ,

The led gets the bit instruction from the panel to turn on , so in that case either you are at the wrong head or the led has failed.
I would view each device that is suspect and press key 2 which will turn on the led to confirm you are at the right device , or use a test set , Apollo hochiki , don't know what you are working on ?

It sounds more like corruption to me so access panel in commission mode , enter setup bring up the log section press change key and alter to diagnostic mode , put panel back to normal and leave it half an hour , when you view the log it will then give you indication with any devices that are playing up. However don't forget to put the log back to normal status from diagnostics.
Thanks for the advice, but we were definitely going to the correct detectors. Problem is now sorted.

It seems that a motherboard problem can cause this (according to morley tech) Also a faulty board can cause, non-existent open circuits, and non-existent earth faults.

Anyone else experiencing the same problems with morley panels?? This is the third panel to go down in a month. All panels were installed circa 1999.

Graeme

  • Guest
Yet another Morley problem
« Reply #8 on: July 29, 2008, 06:29:47 PM »
i have lost all faith in Morley and will never use them again for new projects

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Yet another Morley problem
« Reply #9 on: July 29, 2008, 06:51:54 PM »
Quote from: Graeme
i have lost all faith in Morley and will never use them again for new projects
Come on Grame! because of just a faulty card? they still reliable mate! If you have just purchased a brand new panel from Morley, you still have got warranty of replacement do you? Faulty card can happen to any make mate!

Why not seeing the problem the other way round, I used to see engineers fitting loop cards while the system is powered up, when they fail to operate they wash hand straight away claiming it is a faulty card…

I think it is not that easy to blame some trade marks because of some minor deficiencies

Graeme

  • Guest
Yet another Morley problem
« Reply #10 on: July 29, 2008, 07:59:56 PM »
benz

not got anyhting to do with this topic but with my past and present experiences with product and after sales.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Yet another Morley problem
« Reply #11 on: July 29, 2008, 08:20:23 PM »
Quote from: Graeme
benz

not got anyhting to do with this topic but with my past and present experiences with product and after sales.
Alright, sorry for miss-interpreting then... but the only thing I do agree with, regardless of the product itself, is that Morley technical support is so ....., I have never got them straight forward, they are most of the time either in annual leave, meeting or lunch time... etc …

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Yet another Morley problem
« Reply #12 on: July 29, 2008, 08:29:16 PM »
We had similar problem many years ago, and in number of occasions, it was with HAES panel, the panel displays i.e. ‘zone 1’ in fire condition, and alarm was going off for no substantial reasons, even ‘zone 1’ circuit was physically disconnected, the Tech support of HAES company that days agreed to replace the PCB card straight forward.

Graeme

  • Guest
Yet another Morley problem
« Reply #13 on: July 29, 2008, 09:31:51 PM »
Quote from: Benzerari
Quote from: Graeme
benz

not got anyhting to do with this topic but with my past and present experiences with product and after sales.
Alright, sorry for miss-interpreting then...  …
no worries.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Yet another Morley problem
« Reply #14 on: July 30, 2008, 08:56:13 AM »
Quote from: Benzerari
Quote from: Graeme
i have lost all faith in Morley and will never use them again for new projects
Come on Grame! because of just a faulty card? they still reliable mate! If you have just purchased a brand new panel from Morley, you still have got warranty of replacement do you? Faulty card can happen to any make mate!

Why not seeing the problem the other way round, I used to see engineers fitting loop cards while the system is powered up, when they fail to operate they wash hand straight away claiming it is a faulty card…

I think it is not that easy to blame some trade marks because of some minor deficiencies
I'd have to agree with Grahame on this one - given the choice I wouldn't touch them with a 12 foot barge pole now as there are way too many software issues of late and panel problems.
They USED to be a very reliable option and were our preferred panel for open protocol but not anymore.
For tech support you'd be better ringing ADVANCED and talking to one of the ex-Morley guys there (only joking but about as much use as phoning MORLEY)!