Benzerari
What you need to do is remove end 2 of the loop from the panel and then allocate it. The loop will then stop at the fault either open circuit or short circuit.
You can the using the test engineer function 'find device'. This lets you flash the light on the head or it will sound a sounder or action an interface.
Find the device which the loop stops at, then you know its either the device that is found or the next one on the loop.
Thanks skelffie for this info;
This is the same procedure when dealing with any open protocol system where the software is available, the Gent system case is a bit different, If I allocate the loop with one end disconnected would that delete the location text of the other side of the loop? If Yes that would not be my best choice then, for the simple reason that I haven't got Gent software with the previous back up, to re-instate every thing back to normal...
The other night mare is that when taken over this sites, we have done 100% test and lot of location text were found wrong, we assumed the system is been upgraded several times without updating the right location text, I mean we found the location text is a bit moved forward or backward of 3-4 addresses ... ( soft addressing sort of problems ).
None is perfect !