Fairly minimal. Most of it seems to be updated to take into account other new standards, i.e. reference to any HTM will be the most recent HTM.
Acknowledgement of L5 systems possibly being localized detection to compensate for departure from guidance.
A half page modification in chapter 11, system components. Mainly what different detectors and cables etc should conform to.
A bit on detection zones and MCPs in stairwells.
A bit extra on visual alarms.
Reference to accessibility requirements under building regs re: impaired hearing.
Reference to mounting switches no higher than 1.2m due to guidance in Bregs ADM. It still suggests 1.4m as standard though.
An interesting one, possibly important to know if you are a designer/installer: NOTE 4 In a Category L2 or L3 system, detectors in rooms opening onto escape routes are provided only to give a warning of fire before it affects the escape routes. Detection in voids above or below the rooms might not be necessary for this purpose (e.g. if fire resisting construction separates a void from the adjacent escape route).
Various other stuff on voids.
Acknowledgement that cables should be secured in such a way that they remain secured for the same duration they are intended to survive in a fire. (And also of the risk to firefighters of collapsing cables)
A bit on rcd's.
Modification to 12 month test.
That is about it.