The dry riser solution is in ADB.
16.3 Note 1 : If the provisions in paragraph 16.2 or 16.3 (the 45m from all points...) cannot be met, a fire main should be provided in accordance with paragraph 15.3.
This is a riser within the building with access to the inlet no more than 18m away,(i.e. Inlet could be near the gate.) not a hydrant. Since this would be accepted under ADB, then he should speak to the FRS to see if they want to go through the motions of connecting to a riser in a 2 storey building, or if running 1 more length of hose out is more suitable.
Yes I agree civvy- but in practical terms what benefit does it give? (I dont mean to shoot the messenger by the way - I know we feel the same from your own posting)
Why spend good money on a such a pointless and expensive solution? In this case distance from access point to furthest point of floor area is 70m. A compliant layout would be 45m.
So What? 45m is two lengths of hose to run out. 70m is nearly 3 lengths of hose (direct distance). If life is at risk how long does it take to run out threee lengths compared to two? an extra 5 seconds?
How long does it take to find the fire main inlet, smash the glass, unroll a hose and couple, run in to the other end of the main, find the outlets, couple another length of hose, flake it cos you are on top of the job, then have the problem of all the kinks as you charge the hose- at least 60 seconds longer.
Sometimes there is an attitude amongst inspectors that "You are not compliant in this area so what will you give me in exchange?" - thats the type who would insist on a fire main in this situation. On the other hand of course it could also be the fault of the architect or fire consultant for not digging in their heels and arguing for common sense.