Fire Safety Provisions needed in Boiler Room?
« on: October 15, 2008, 11:14:28 AM »
Have a gas boiler in a small room approx. 3sq.m, to heat a shop/commercial unit.  The room is 60 min fire resisting construction with FD60S door and heat detector.  There will be a passive wall vent in the external wall.  BS5588 suggests that smoke venting is required from  a boiler room, but doesnt say what type/size it should be.  Do I have enough safety provisions here? Do you think I need to provide an automatic smoke vent or suppression system?

Thanks

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Fire Safety Provisions needed in Boiler Room?
« Reply #1 on: October 15, 2008, 01:47:35 PM »
Sounds a bit over the top to me.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Fire Safety Provisions needed in Boiler Room?
« Reply #2 on: October 15, 2008, 03:25:25 PM »
Sounds fine as it is- many boilers are quite safely installed on the wall of the premises they serve without being enclosed in a fire resisting compartment. Depends on the size of the installation and the use of the premises.

Main thing is not to allow combustible storage to accumulate in the boiler room- out of sight out of mind.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Fire Safety Provisions needed in Boiler Room?
« Reply #3 on: October 15, 2008, 03:28:32 PM »
Quote from: muggins
Have a gas boiler in a small room approx. 3sq.m, to heat a shop/commercial unit.  The room is 60 min fire resisting construction with FD60S door and heat detector.  There will be a passive wall vent in the external wall.  BS5588 suggests that smoke venting is required from  a boiler room, but doesnt say what type/size it should be.  Do I have enough safety provisions here? Do you think I need to provide an automatic smoke vent or suppression system?

Thanks
Bear in mind that oil burners on fire would produce more smoke than a gas burner which would produce very little other than that from any surrounding combustibles.
We're not Brazil we're Northern Ireland.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Fire Safety Provisions needed in Boiler Room?
« Reply #4 on: October 15, 2008, 03:50:58 PM »
But they may explode blowing the whole building to kingdom come

Midland Retty

  • Guest
Fire Safety Provisions needed in Boiler Room?
« Reply #5 on: October 15, 2008, 03:53:29 PM »
Hello Muggins

You would not require any additional precautions over and above those you have already mentioned . Smoke vent / supression system would certainly not be required.

Offline muggins

  • Newbie
  • *
  • Posts: 15
Fire Safety Provisions needed in Boiler Room?
« Reply #6 on: October 15, 2008, 04:27:29 PM »
Thanks for your help

Chris Houston

  • Guest
Fire Safety Provisions needed in Boiler Room?
« Reply #7 on: October 15, 2008, 04:57:08 PM »
I see boiler rooms day in and day out and can't remember any that has smoke vents.

A 60 minute compartment with fire detection sounds pretty good to me.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Fire Safety Provisions needed in Boiler Room?
« Reply #8 on: October 15, 2008, 05:54:31 PM »
Ventilation is obviously needed for the efficient combustion of the burner.
We're not Brazil we're Northern Ireland.