« on: November 24, 2008, 09:53:19 PM »
Since an L3 system should always incorporate the requirements of an M system I was under the impression that although correct L3/M shouldn't be stated as a category of system to avoid confusion.

Am I correct in thinking this or can an L3/M system actually be a combination of systems on a project e.g Multistorey car park requiring L3 in stairwells and M in the parking areas?
« Last Edit: November 24, 2008, 09:56:10 PM by g4vjc »

Graeme

  • Guest
Re: L3/M
« Reply #1 on: November 24, 2008, 10:32:33 PM »
i might be wrong but if you are puting afd in a specific area it would come under M/L5

or would afd in the escape routes stairwells only come under L4?
« Last Edit: November 24, 2008, 10:42:34 PM by Graeme »

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: L3/M
« Reply #2 on: November 24, 2008, 11:28:38 PM »
There is no such thing really as L3/M for the reasons you stated.
Colin Todd, C S Todd & Associates

Offline g4vjc

  • Newbie
  • *
  • Posts: 8
Re: L3/M
« Reply #3 on: November 25, 2008, 03:34:57 PM »
The system has been specced as per my original post.

So it should really be classed as an L5 and not an L3/M as there is no such thing as an L3/M?

Graeme

  • Guest
Re: L3/M
« Reply #4 on: November 25, 2008, 04:09:32 PM »
i would say yes to M/L5