Author Topic: Apollo Ancillary Sounder  (Read 19117 times)

Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Apollo Ancillary Sounder
« on: November 27, 2008, 07:03:59 PM »
This has been bugging me for a while, We use these quite a lot on larger installs.

Are they compliant with BS?? As far as I'm aware they don't report a fault condition to the panel, unlike the XP95 equivalent.
I found a faulty one today during a sounder test, just didn't sound at all, no fault on the control panel..

Any one have any ideas??

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Apollo Ancillary Sounder
« Reply #1 on: November 27, 2008, 08:49:42 PM »
This has been bugging me for a while, We use these quite a lot on larger installs.

Are they compliant with BS?? As far as I'm aware they don't report a fault condition to the panel, unlike the XP95 equivalent.
I found a faulty one today during a sounder test, just didn't sound at all, no fault on the control panel..

Any one have any ideas??

Can you display its picture or at least its link ?

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Apollo Ancillary Sounder
« Reply #2 on: November 27, 2008, 10:44:46 PM »
This has been bugging me for a while, We use these quite a lot on larger installs.

Are they compliant with BS?? As far as I'm aware they don't report a fault condition to the panel, unlike the XP95 equivalent.
I found a faulty one today during a sounder test, just didn't sound at all, no fault on the control panel..

Any one have any ideas??

The ancillary base sounder must be installed under a detector. To physically 'remove' it from the circuit would also require removing the detector which will obviously bring up a 'fault' condition. This is the best you will get.

Is this good enough monitoring? Well imagine installing an electronic sounder (non-addressable) on to a standard monitored sounder circuit - If someone removed it and then reconnected the wires to the circuit you wouldn't be any the wiser. No different from the ancillary sounder.

As for actual reporting of the device not working, this is no different, again, in comparison to a normal sounder. The first you know it's not working is when you physically test it and you can't hear it.

Therefore it is my opinion that the Apollo ancillary base sounder meets BS recommendations equally well as a standard (non-addressable) sounder.

If you want a 'better' loop-powered sounder then choose the Integrated Base Sounder. This has voume control, group addressing and a self-testing facility although, of course it uses an extra address (whereas the ancilary doesn't) and it doesn't cost much morethan the ancillary!
« Last Edit: November 27, 2008, 10:46:27 PM by Wiz »

Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Re: Apollo Ancillary Sounder
« Reply #3 on: November 27, 2008, 11:53:56 PM »
Cheers Wiz, that puts a few concerns to rest.

Benz this is it.
http://www.apollo-fire.co.uk/45681-276.html

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Apollo Ancillary Sounder
« Reply #4 on: November 28, 2008, 02:05:11 AM »
Just to pick up and agree with one of Wiz's points - I had a bell fail during maintenabe yet the panel indicated no fault as it only monitored for open or short circuit on the sounder circuit.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Apollo Ancillary Sounder
« Reply #5 on: November 28, 2008, 08:31:46 AM »
As itis triggered from the remote LED output of the detector head and to actually remove the sounder would mean removal of the head as Wiz said it does fully comply.

Apollos statement when I challenged them on this was the above, plus if the integral parts failed after the monitoring of the circuit on any device that wouldn't produce a fault on a standard sounder anyway.

I think it's a bit of a grey area, but they are damn cheap !!!!
** Knowledge is power, I'm still working on both **

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Apollo Ancillary Sounder
« Reply #6 on: November 28, 2008, 10:15:46 AM »
No cause and effect possible , I bet a few people have been caught out here then.
Its time to make a counter attack !

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Apollo Ancillary Sounder
« Reply #7 on: November 28, 2008, 10:25:25 AM »
Indeed.  Also, you cannot pulse the sounder, nor is the sounder syncronized !!
** Knowledge is power, I'm still working on both **

Graeme

  • Guest
Re: Apollo Ancillary Sounder
« Reply #8 on: November 28, 2008, 10:56:54 AM »
and they don't work on C-tec AFP as you cannot tell the panel there is a sounder with the detector.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Apollo Ancillary Sounder
« Reply #9 on: November 28, 2008, 04:40:18 PM »

Benz this is it.
http://www.apollo-fire.co.uk/45681-276.html

We used to call it just 'sounder base', it can be fitted above the detector or on its own, but with additional cover, the conventional version behaves just like a normal Roshni sounder or bell in terms of fault monitoring by means it is like terminal block to inssure continuity of the loop, by removing it, the panel would sees open circuit, and by closing back the loop, the panel clear off the open circuit fault, as the panel keeps looking for the EOL only... etc, if you want to test it individually, you have to test it with spare battery + to + and - to -... etc and see if it sound... etc

If you say it doesn't comply to BS... , so any normal conventional sounders such as Roshni, Squashni, Horn, cryer, Bell, wouldnt comply too! which is not the case


Offline JonnyG

  • Newbie
  • *
  • Posts: 49
Re: Apollo Ancillary Sounder
« Reply #10 on: November 28, 2008, 05:15:15 PM »
Benz, I didn't say it didn't comply with BS.  I was asking if it did!!!! ;D

Offline Rosjes

  • Newbie
  • *
  • Posts: 29
Re: Apollo Ancillary Sounder
« Reply #11 on: November 28, 2008, 05:17:35 PM »
A point that bigfella touched upon, the sounder works off the remote led o/p. If you remove the head when in alarm the sounder stops so surely if the ancillary base used the head ought to be locked!

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Apollo Ancillary Sounder
« Reply #12 on: November 28, 2008, 05:35:22 PM »
Isn't the ancilarry base sounder only a local sounder, in that it only works when the associated detector operates?
This being the case it doesn't operate on a general fire alarm.
Might be wrong though!

Offline Rosjes

  • Newbie
  • *
  • Posts: 29
Re: Apollo Ancillary Sounder
« Reply #13 on: November 28, 2008, 05:46:42 PM »
Buzzard, all ancillary base sounders operate in a fire condition.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Apollo Ancillary Sounder
« Reply #14 on: November 28, 2008, 06:10:07 PM »
Literature confusing then http://www.apollo-fire.co.uk/editpics/270-1.pdf .
I know the integrated and intelligent sounders are the most common ones used though.