Author Topic: Battery Calculation  (Read 6978 times)

Offline FireFox

  • Newbie
  • *
  • Posts: 3
Battery Calculation
« on: December 01, 2008, 11:52:45 AM »
Please find attached battery calculation, for a Secutron 2900 FACP fire alarm system, given by an installer. As far as I know, the standby current and alarm current for all the components need to be considered. But here current consumption of all the components are not considered in alarm condition. Is this calculation correct? Thanks in advance

Regards

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Battery Calculation
« Reply #1 on: December 01, 2008, 01:19:50 PM »
I don't understand why they only calculate the alarm load by (3.27) by 5 minutes.

The minimum recommendation is 30 mins.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline FireFox

  • Newbie
  • *
  • Posts: 3
Re: Battery Calculation
« Reply #2 on: December 01, 2008, 01:26:26 PM »
This was installed as per NFPA standards:

4.4.1.5.3.1 Unless otherwise permitted or required by 4.4.1.5.3.1(A) or 4.4.1.5.3.1(B), the secondary power supply shall have sufficient capacity to operate the fire alarm system under quiescent load (system operating in a nonalarm condition) for a minimum of 24 hours and, at the end of that period, shall be capable of operating all alarm notification appliances used for evacuation or to direct aid to the location of an emergency for 5 minutes.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Battery Calculation
« Reply #3 on: December 01, 2008, 01:32:46 PM »
Here you go..., a good difference between NFPA 72 and BS 5839 in terms of batt. calculations...

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Battery Calculation
« Reply #4 on: December 01, 2008, 01:35:49 PM »
Also.... the alarm currents they are quoting for the sounders etc are huge.......!

Its not clear that the total standby current has been taken into account, or any additional alarm load integral to the control equipment.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline FireFox

  • Newbie
  • *
  • Posts: 3
Re: Battery Calculation
« Reply #5 on: December 01, 2008, 01:46:09 PM »
I think this (attached) should be the format which has to be followed. Kindly correct me if I'm wrong.
« Last Edit: December 04, 2008, 08:49:19 AM by FireFox »