Author Topic: BS 9999 / ADB - Discounting of Stair rule  (Read 13326 times)

Offline ST1878

  • Newbie
  • *
  • Posts: 27
BS 9999 / ADB - Discounting of Stair rule
« on: December 02, 2008, 01:13:18 PM »
Has anyone come across the apparent anomoly for the discounting of stairs in sprinklered buildings yet?
BS 9999 para 18.3.2 states "the stair discounting process DOES NOT APPLY to a building fitted with a sprinkler system".
This appears to be at odds with the earlier DD 9999 para 8.8.3.2, and the current ADB para 4.20 which state "stair discounting ALSO APPLIES to a building fitted with a sprinkler system, unless the staircase is lobbied or pressurised".

We have requested clarification from the relevant bodies, but have yet to receive an explanation to the difference, and we have now had proposals from an AI referring directly to the para in the new BS.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #1 on: December 02, 2008, 01:18:11 PM »
I'm not sure if that counts as an anomoly, The are different codes - they will say different things.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #2 on: December 02, 2008, 06:27:59 PM »
Sprinklers are invoke and the answer to all our prayers.  As above, different code, different standard, its out there for use and people will use it.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #3 on: December 02, 2008, 11:57:19 PM »
if the nat west tower is sprinklered it would probably only need one 530mm exit for compliance with BS 9999.
Colin Todd, C S Todd & Associates

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #4 on: December 03, 2008, 12:23:19 AM »
It is
Its time to make a counter attack !

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #5 on: December 03, 2008, 09:27:36 AM »
You would still need to discount a storey exit wouldnt you?

Davo

  • Guest
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #6 on: December 03, 2008, 12:22:27 PM »
What does BS 7974 have to say on this dilemma? ???

I for one would not want a designer to put one less stair in because you don't need to discount (IMO)

Davo

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #7 on: December 03, 2008, 12:27:35 PM »
Well if you need two storey exits then I think you will need a stair next to it. Iether that or issue parachutes.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #8 on: December 03, 2008, 06:15:11 PM »
As we are all aware fire safety is joined up thinking and stair discounting is not a subject of its own, it also includes travel distance and numbers of people.  What 9999 does is limit in some circumstances the numbers of exits and stairs that are needed and substantially in some areas.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #9 on: December 04, 2008, 01:04:23 AM »
Parachutes, brian................ HMMMMMMMMMM Could that be a new business opportunity?
Colin Todd, C S Todd & Associates

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #10 on: December 04, 2008, 01:52:27 PM »
No mate - Fire evac parachutes have already been patented. They tried flogging them after 9/11

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #11 on: December 04, 2008, 09:36:50 PM »
Ah Brian, it just goes to show there is nothing new in this world. No wonder, I/Os keep rediscovering what we knew 30 years ago. Should I just keep my money in intumescent strip manufacturers then?
« Last Edit: December 04, 2008, 11:58:16 PM by colin todd »
Colin Todd, C S Todd & Associates

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #12 on: December 04, 2008, 09:57:01 PM »
Evacuchute. Do you think these would be suitable for old peoples homes





http://www.evacuchute.com/products_build_civilian.html
I refuse to have a battle of wittts with an unarmed person.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #13 on: December 04, 2008, 11:59:28 PM »
Yes it would give the wrinklies the thrill of their (imminently ending) life.
Colin Todd, C S Todd & Associates

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: BS 9999 / ADB - Discounting of Stair rule
« Reply #14 on: December 05, 2008, 08:21:58 AM »
I would love to see someone write that in to a risk assessment.

Imagine the look on the IO face when he does an audit.
I refuse to have a battle of wittts with an unarmed person.