The formula you quoted can be boiled down to three quarters of the width of the stairs plus 5mm per person for all those coming from the ground floor.
You are right that this is anomalous within the context of 9999 because a different width per person is probably applicable. It's not perfect, this 9999. But it's a best guess for the time being (just as are all other fire safety numbers). You'll find a similar anomaly in the section on shopping mall exit widths, they're still basing mall exits on 5mm per person.
At least these little quirks are erring on the side of safety. Also, they are simple (increased accuracy would bring increased complexity).
Another thing to note about the formula you quoted. Even if only 50 people are joining the flow from the ground floor you still apply the 5mm per person and that doesn't seem to sit right with the fact that you cannot use 5mm per person for less than 220 people. But the formula does make sense because those few people that are joining the flow from the ground floor are joining a larger flow from the upper storeys which, hopefully, takes the total above 220.
Why do you think B2 in Table 13 should be 4.4?
Davo, is this one of the errors you spoke of?
Stu