Detectors in Chimneys
« on: January 29, 2009, 11:15:28 AM »
I've just been asked a question I don't have the answer to, and wondered if anyone has a solution...

A detector for use within a chimney.

Any ideas, types of detector recommended etc?

Thanks in advance
** Knowledge is power, I'm still working on both **

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Detectors in Chimneys
« Reply #1 on: January 29, 2009, 11:16:53 AM »
I've just been asked a question I don't have the answer to, and wondered if anyone has a solution...

A detector for use within a chimney.

Any ideas, types of detector recommended etc?

Thanks in advance
For what reason?
We're not Brazil we're Northern Ireland.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Detectors in Chimneys
« Reply #2 on: January 29, 2009, 11:28:09 AM »
The site is a fairly old manor house, and they are worried 'something' might catch alight above the fire place in the stack, and they are after an early warning of such an instance.  Obviously the stacks should be regularly cleaned to prevent such instances but this is their request.
** Knowledge is power, I'm still working on both **

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Detectors in Chimneys
« Reply #3 on: January 29, 2009, 12:17:58 PM »
I suppose if you knew what the maximum heat was within the stack from a specific distance you could install heat detection to activate above this (set at a percentage above the ambient) but,that aside,can't think of anything alse.

Graeme

  • Guest
Re: Detectors in Chimneys
« Reply #4 on: January 29, 2009, 01:04:02 PM »
probe heat detector or linear?

This is the first time i have heard of this being asked.

i would however avoid a smoke detector ;D

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Re: Detectors in Chimneys
« Reply #5 on: January 29, 2009, 01:20:53 PM »
Would the budget allow for a flame detector ?

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Re: Detectors in Chimneys
« Reply #6 on: January 29, 2009, 02:57:04 PM »
May be cheaper to line the chimney...

Offline Morri

  • Newbie
  • *
  • Posts: 14
Re: Detectors in Chimneys
« Reply #7 on: January 29, 2009, 03:02:40 PM »
Agree with Mr P, remove the hazard if it is a genuine concern

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Detectors in Chimneys
« Reply #8 on: January 29, 2009, 05:48:55 PM »
Would the budget allow for a flame detector ?
Dirty enviroment and,depending where they want protection to be located,false alarms liable.

Offline John Webb

  • Hero Member
  • *****
  • Posts: 838
Re: Detectors in Chimneys
« Reply #9 on: January 29, 2009, 08:57:02 PM »
I think the best solution would be industrial standard sheathed thermocouples. These can be easily monitored and with an Iconal or stainless steel sheath will resist soot, heat and other corrosive gases. We used them regularly in large fire tests to measure gas and flame temperatures and they rarely needed replacement. Not quite to BS5836 but as that doesn't quite cover this particular area anyway...
John Webb
Consultant on Fire Safety, Diocese of St Albans