Today I have come across something I have not seen before and would be interested in your views.
A computer room is protected by an HFC gas system operated by conventional detectors on double knock. In addition am HSSD system has been installed, sampling the floor and ceiling voids- the floor appears to be used as a plenum for the main air conditioning system. Not sure about the ceiling void.
Suspended from the ceiling are conventional cooler units drawing air in at the base - about 450mm below ceiling level and blowing it out at the front of the unit across the underside of the false ceiling.
Immediately beneath the inlet on the base of the unit a section of HSSD sampler pipe, with a hole drilled every 300mm has been installed, in the path of the air entering the cooler. The sampler pipe is about 30mm below the inlet grille and on some coolers the holes face the base of the cooler, on others the holes face the room.
Now I dont know if I have had a sheltered upbringing or whatever- but I have never seen this done before and wonder, bearing in mind the relative velocity of the air as it aproaches the cooler and the velocity of air in the sampling pipe whether it will provide any useful early warning of fire. And which way the holes should face?
I have not yet been able to ascertain whether or how the HSSD is interfaced to the fire alarm , the suppression system or the HVAC system.