Soak Test after modification to 5839 FAS
« on: May 17, 2009, 11:02:25 AM »
Hi All,

I am currently dealing with a project in its final stages previously un-notified to me, where the fire alarm system has been modified, (additional 20 or so detectors added to an existing system). BS 5839 explains that a soak test is required for a system with more than 50 detectors. The system, even though I haven't counted them must have in excess of 50 detectors including the original fitted SD.

Does this mean that a soak test is required, even though the added number of detectors is less than 50. In other words is a soak test required for the added and original being over 50.

I believe at this stage the system is closed protocol and the software is also going to be re-programmed for the additional detectors.

Any help would be useful.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Soak Test after modification to 5839 FAS
« Reply #1 on: May 17, 2009, 11:53:48 AM »
The answer is no.

50 or more 'new' detectors

Same goes with a commissioning certificate and design certificate, you will be certifying the new installation