Author Topic: Repeater Panels  (Read 5760 times)

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Repeater Panels
« on: May 19, 2009, 10:29:49 AM »
Hi

Can someone tell me if there is a need under 5839 to have repeater panels with an LI system for a large building...ie a hospital

Ta

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Repeater Panels
« Reply #1 on: May 19, 2009, 10:32:10 AM »
Under HTM I think it says repeater panels are to be provided at nurse stations.  This would be a minimum of course
** Knowledge is power, I'm still working on both **

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Repeater Panels
« Reply #2 on: May 19, 2009, 11:37:27 AM »
Thanks Big fella

 i've just scanned through HTM 05-03 Part B and can't see any reference to repeater panels at all

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Repeater Panels
« Reply #3 on: May 19, 2009, 11:51:46 AM »
Depends on how the lads with the big red things with blue lights enter the building. ;)
Its time to make a counter attack !

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Repeater Panels
« Reply #4 on: November 10, 2009, 11:03:00 AM »
sorry to drag this again...but does anyone know where in the HTM that it says repeater panels are required?

Thanks

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Repeater Panels
« Reply #5 on: November 10, 2009, 11:47:32 AM »
HTM 05 03 Part B: 4.33

Additional control and indicating equipment,
capable of displaying the location of an alarm
incident to a similar degree to that of the main
panel, should be provided in each and every
management unit, and in any case such that the
travel distance to an indicator panel does not
exceed 60 m. Further control and indicating
equipment should be provided where required
by local evacuation procedures; in particular, a
repeat indicator panel should be provided at the
evacuation control point of any escape bed lift(s).
This should be the subject of consultation

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Repeater Panels
« Reply #6 on: November 10, 2009, 12:14:40 PM »
Thanks Civvy...appreciated mate