Author Topic: Gas supply valves linked to fire alarm system  (Read 45722 times)

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #15 on: July 03, 2009, 09:26:11 AM »
Owen66. thank you for the link.

I couldn't access it directly from your post but by messing around with the address I found it!

Just in case others have problems I've added the link I used here:

http://www.teachernet.gov.uk/_doc/12199/BuildingBulletin100_OnlineVersion.pdf

You are obviously right about the document I found to be just the consultation document. It's a shame no-one has removed this out-of-date info!

In the document on teachernet I would suggest that the guidance is still not clear and this raises a further issue.

Most of the gas solenoid valves interfaced to fire alarms operate on any fire condition. This causes so many problems in so many establishments whereby any unwanted alarm causes the boilers to shut down and usually requires someone (at cost and time) to reset them!

I believe that the guidance could be suggesting that it is only a fire condition detected in a boiler house that should shut down the boiler!

If this is the case, and if it also applies to hotels, then my failure to be provided with a hot shower and cooked breakfast in a leading hotel in Birmingham a couple of years ago because the gas had been shut off by a faulty corridor smoke detector and no-one knew how to reset the boiler was all down to mis-interpretation of guidance documents.

I'm still fuming about missing breakfast!


Offline Owen66

  • Jr. Member
  • **
  • Posts: 53
Re: Gas supply valves linked to fire alarm system
« Reply #16 on: July 06, 2009, 05:20:35 PM »
Well yes, a global command will tend to shut down the solenoid for any activation of the fire system.

A simple addressable system however should be capable of selectively programming the I/O unit such that activation only occurs from pre determined devices operating - heating chamber heat detection and associated Break glass units.

Same goes for any building type I guess - part of the fire strategy.

Sorry about breakfast BTW - but that's Brum for you

Regards

Owen

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #17 on: July 06, 2009, 08:40:02 PM »
Owen66, thanks, but the question isn't how to achieve it!

My question is why do we do it, not how can we do it?

My last post was confirming that the document you directed me to also actually indicates that it is only the detector in the boiler house that should operate the gas solenoid valve and not any alarm condition from anywhere (which is often the case)

My original question stands.






Offline Owen66

  • Jr. Member
  • **
  • Posts: 53
Re: Gas supply valves linked to fire alarm system
« Reply #18 on: July 07, 2009, 12:05:49 PM »
Not sure as to the why Wiz although I can see the logic in removing a fuel source in the event of a fire that is likley to be in close proximity to that fuel source (or perhaps in high rise etc where vertical gas mains exist).

The requirement does seem to occur with remarkable frequency in all sorts of documents but based on a few I've looked at it seems that the requirement is only for shutdown on local activation (the old thermal link approach ) - this seems to have evolved into a global shutdown situation for some reason. Insufficient time allowed to programme the fire panel perhaps - or vague requirements in the first place.

I would have thought a building fire startegy would define this in some deatil but sadly not usually the case.

Regards

Owen

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Gas supply valves linked to fire alarm system
« Reply #19 on: July 07, 2009, 12:56:51 PM »


http://www.bsdlive.co.uk/story.asp?storycode=3060154

This document refers to the shuttingdown of the gas supply on ventilation failure within the extract hood....

I wonder if this is a case of chinese whispers over the years....
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #20 on: July 07, 2009, 01:25:31 PM »


....................I wonder if this is a case of chinese whispers over the years....

That's why I originally raised the subject.

Seems no-one knows. Even in this supposedly super forum.

Shame no gas monkeys have put in any input to the discussion. Or it could be that they don't know either.

I pray for the day that there are one set of clear easily understandable set of rules and regulations for every building/room type and every situation (I don't believe that every situation has to be so different!). Then everyone would know what they are doing and why.

Until that day, bullsh*t will continue costing this country £Billions !

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Re: Gas supply valves linked to fire alarm system
« Reply #21 on: July 16, 2009, 04:52:53 PM »
The major kitchen fire suppression manufacturers all advise an automatic shutdown of the gas supply be linked to their systems then upon activation of the fire suppression system this would ensure there is not a build up of gas within the area once the fire is extinguished. Obviously there could still be a heat source in the area which could ignite any gas build up or if there are appliances not protected by the nozzles and are on fire they don't ignite the gas from other appliances. (What's that I hear you all say? Surely no  :-X would place an appliance without protection??? Oh yes, sad to say 'tis oh so true - anyone need photo's?? There are some classics out there..)  
It also ensures that if the evacuating staff forget or cannot physically get to the shut off valve/switch then the gas will be cut off upon their evacuation.
The shut off can be mechanical or electrical (which then would be linked to the F/A)

Which is nice if your a fireman type chap rushing in to a kitchen to check out the latest salamander or fryer in your local restuarant or Big Macs.
Some of the locations of the manual gas shutoff switches beggar belief. Try knocking off the gas at 2-3' from a blazing fryer.

The system manufacturers also advise them (the suppression systems) to be linked to the F/A via a n/o link. Both the gas shut off and F/A link are activated upon system release simultaneously.


That may answer the original enquiry. I'm no gas monkey, just a humble Ansul monkey working long nights this week and short of sleep.
« Last Edit: July 16, 2009, 05:35:26 PM by Psuedonym »
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #22 on: July 16, 2009, 05:30:54 PM »
Thanks for the input psuedonym (is that really your name?)

I think we all understand the reasons why these shutdowns could be required.

But are you aware of any authorative guidance documents or recognised standards that state the specific requirements?

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Re: Gas supply valves linked to fire alarm system
« Reply #23 on: July 16, 2009, 05:42:23 PM »
No, of course not. Its a psuedonym you know.

I will get hold of the regs and let you know when I can dig them out. The kit is US and their info relates to the UL standards (UL300), but I'm pretty sure we have the equivalent standard over here. The insurance firms also advice the same so there must be somthing lurking around. I just can't remember what! It's old age.......
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #24 on: July 17, 2009, 08:35:06 AM »
Thanks for the input psuedonym (is that really your name?)

No, of course not. Its a psuedonym you know.

I'm obviously not as funny as I think I am!  :(

Offline Owen66

  • Jr. Member
  • **
  • Posts: 53
Re: Gas supply valves linked to fire alarm system
« Reply #25 on: July 17, 2009, 09:53:55 AM »
Well I had a chuckle, Wiz   ;D

Owen

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #26 on: July 17, 2009, 11:59:22 AM »
Thanks Owen!




Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Gas supply valves linked to fire alarm system
« Reply #27 on: July 17, 2009, 01:38:40 PM »
I think as the discussion evolves we are seeing that:

a) Specific standards for specific situations (e,g, cooker hood supression, schools guide) mandate the use of an automatic gas supply shut off

b) However as far as an across the board requirement (i.e. independent of a specific risk situation in a building or part thereof) for gas valve shut off goes there is no actual requirement/recommendation, it's just something done because 'that's what we do'
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Re: Gas supply valves linked to fire alarm system
« Reply #28 on: July 18, 2009, 10:20:22 AM »
Wiz, the only regs regarding fuel i.e. gas/electric shut off to kitchen equipment from a fire suppression sytstem is LP1223 2.2 section 5. That with UL300 i.e. US equipment listings which as US kit we adhere to so as to be compliant,
The is no legislation for fire suppression - catering, for F/A link up or notification from installer/surveyor or the manufacturers' specification information advising links are possible and the procedures for installing switch gear in their control panels.
That plus pointing out to the client the advantages of a link. Most insurance firms, if aware of the possibilities, also advise a link.

Unfortunately "risk assessors" simply tick the  Fire Suppression Installed? Y/N box. But that's another debate, one which I had with a duty manager this morning while the rest of sensible world was tucked up asleep!
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Gas supply valves linked to fire alarm system
« Reply #29 on: July 18, 2009, 03:55:47 PM »
Thanks both to AnthonyB and psuedonym for their recent answers.

It seems that the fire alarm system operated gas cut-off solenoid valves commonly installed all over the place recently have been installed because of (i) 'findings' of a risk assessment (ii) recommendations from a manufacturer of a specific piece of equipment based on standards that may not apply to the u.k (iii) because it seems a good idea/that's what we did on the last job scenario.