Well according to Table A2 Cat A/B/C can be applied to the following type of doors at least...
4. Forming part of the enclosures of a stairway that forms part of means of escape (other than stairways described in items 2 and 3 and
stairways in dwellings) A, B or C In the case of Category C, only if the critical signal path, and any wiring from non-fire alarm control equipment to the release mechanisms, fails safe.
5. Forming part of the enclosures of a fire-resisting lobby to stairways described in items 2 to 4 inclusive A, B or C In the case of Category C, only if the critical signal path, and any wiring from non-fire alarm control equipment to the release mechanisms, fails safe.
6. Subdividing corridors A, B or C
7. Any fire door in a dwelling, other than in the common parts of an HMO A, B or C
8. Any other positions, including (but not limited to) fire doors to rooms A, B or C
.........and the following type of building
1. Common places of work, not generally occupied by significant numbers of members of the public (e.g. offices, factories and warehouses), where staff are trained in the fire safety provisions in the building A, B or C
..........So to me it seems that Acoustic units could be used on quite critical doors protecting employees and the public alike and as you say, suddenly the release mechanism needs to be in range of two sounders !
I'd lay odds 99% of dorguards installed in the country aren't within earshot of two sounders. Perhaps we should contact them and ask why they don't mention it in their installation instructions ?
Suddenly the cost saving device might not be so appealing.....!