7273 pt 1
Clause 8.2 says
"The wiring of for the extinguishing system should conform to the recommendations given in BS 5839 pt 1:2002 Clause 26 for cables of standard fire resistance."
So I would take that to include the mains supply and means of isolation.
Also, 6266: 2002
6.3.2 Circuit integrity for risk Category D and Category E installations Where continuity of service from the electronic equipment is required for life safety reasons or to prevent unacceptable interruption to operations, additional precautions might be necessary to ensure that power and data cables are not unduly susceptible to damage by fire. Power cables should therefore be of a fire-resistant type, and conform to Category CWZ of BS 6387:1994.
So having carried out the RA, if the shutdown circuit is considered "critical" then the field wiring to which you refer should be fireproof......... in my opinion..