We are providing interfaces to "open" sliding doors in a church. The manufacturer tells me there is a pair of wires that when shorted will cause the doors to open (powered by an internal battery) therefore we can link a fire alarm relay to this pair, and wire a manual release (green breakglass) in parallel.
If we take power completely off the doors they will not slide open, simply be in a position to slide freely.
Is this acceptable in respect of the following clauses...
9.4 The design or configuration of electronically operated locks or striking plates should be such that power is not required in order to unlock any door. If fitted to fire-resisting doors, the lock, latch and locking plate should meet the requirements for BS EN 12209:2003,
Grade 1 in respect of fire resistance; hardware for the door should meet the requirements for BS EN 1527:1998, Grade 1 in respect of fire
resistance.
9.5 Powered sliding doors on means of escape should be installed in accordance with BS 7036-2. The configuration of the release
arrangements should be such that the doors open in the event of failure of the power supplies that operate the doors.