Author Topic: ADT Conventional MX 4 zone panel  (Read 16343 times)

Offline bibbage

  • Newbie
  • *
  • Posts: 24
ADT Conventional MX 4 zone panel
« on: September 11, 2009, 05:37:53 PM »
Hi

Has anyone got experience of these panels, tried putting one on engineers test today, but couldn't get it to work.
I had the little instruction booklet which about as much use as the panel!

Cheers
Cheers
Bibbage

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: ADT Conventional MX 4 zone panel
« Reply #1 on: September 14, 2009, 05:41:47 PM »
Did you push the button on the pcb inside??

Offline smoke monkey

  • Newbie
  • *
  • Posts: 24
Re: ADT Conventional MX 4 zone panel
« Reply #2 on: September 14, 2009, 10:15:11 PM »
You dont need to use the walk test.
There is nothing stopping you testing lots of devices and then reseting the panel.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: ADT Conventional MX 4 zone panel
« Reply #3 on: September 14, 2009, 10:59:43 PM »
It's handy if you want to walk test the sounders.

Offline bibbage

  • Newbie
  • *
  • Posts: 24
Re: ADT Conventional MX 4 zone panel
« Reply #4 on: September 15, 2009, 05:31:43 PM »
Hi, Yeah I pressed the button inside and the test light lit, but it wouldn't cancel the alarms. Cheers
Cheers
Bibbage

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: ADT Conventional MX 4 zone panel
« Reply #5 on: September 15, 2009, 09:09:10 PM »
Theres something else (obviously!) that you have to do but I just can't remember as it's over 5 years since I worked on one.
Can't even find a soft copy of the manual but have faith!!

Offline spanner

  • Newbie
  • *
  • Posts: 19
Re: ADT Conventional MX 4 zone panel
« Reply #6 on: September 15, 2009, 09:50:50 PM »
is it an MXC 4 zone conventional panel, or one of the old minerva 4 zone conventional panels?

If it is an MXC on the inside back bord there is a black button on the top right hand corner, you have to press and hold that untill the light for test mode comes on.
then you use the front door controls to select what zones you ish to put into walk test (use the return key to scroll and te enter button to enter each zone into test)

if its the old minerva 4, you set the dill switches on the back of the front door for the zones you wish to put into walk test, then press reset.

hope that helps  ;)
The man who smiles when things go wrong has thought of someone to blame it on

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: ADT Conventional MX 4 zone panel
« Reply #7 on: September 16, 2009, 01:49:28 AM »
is it an MXC 4 zone conventional panel, or one of the old minerva 4 zone conventional panels?

If it is an MXC on the inside back bord there is a black button on the top right hand corner, you have to press and hold that untill the light for test mode comes on.
then you use the front door controls to select what zones you ish to put into walk test (use the return key to scroll and te enter button to enter each zone into test)

if its the old minerva 4, you set the dill switches on the back of the front door for the zones you wish to put into walk test, then press reset.

hope that helps  ;)
Aye,that sounds familiar right enough - select each in turn after the internal button.

Graeme

  • Guest
Re: ADT Conventional MX 4 zone panel
« Reply #8 on: September 19, 2009, 10:01:56 AM »
Allen

On a similar note,the panel i spoke about to you recently..should a fault be generated if the aux supply fuse blows?

G

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: ADT Conventional MX 4 zone panel
« Reply #9 on: September 19, 2009, 11:46:31 AM »
Who blew a fuse then?  ::)
TBH I cant remember if the AUX 24 is monitored or not - I really wish that handy CD I had hadn't got broken!

Graeme

  • Guest
Re: ADT Conventional MX 4 zone panel
« Reply #10 on: September 19, 2009, 12:00:51 PM »
nah not guilty.

got a call out to the panel and the aux fuse had blown for no reason. The fault was only picked up as the access control relay is tied into it and all the doors mags were open.