Hydraulic Testing of CO2 Extinguishers
« on: September 30, 2009, 01:19:57 PM »
Hi

Can anyone tell me the frequency of hydraulic testing of CO2 extinguishers?...I seem to recall something like 10 years, 10 years and then 5 years

cheers

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #1 on: September 30, 2009, 03:27:20 PM »
Nope - just ever 10 years no with no requirement for extended services at the intervening 5 year intervals.


Much simpler than what it used to be.....

1st test 10 years from new - unless there is a continuous service history in which case it may be extended to 20 years, but if between years 10-20 the extinguisher requires refilling it must be tested before it can be filled.
2nd test: 10 years from 1st test
3rd & subsequent: 5 years from previous test
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #2 on: September 30, 2009, 06:56:00 PM »
What about 45KG fixed extinguishing cylinders?

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #3 on: October 01, 2009, 10:01:05 AM »
Nope - just ever 10 years no with no requirement for extended services at the intervening 5 year intervals.


Much simpler than what it used to be.....

1st test 10 years from new - unless there is a continuous service history in which case it may be extended to 20 years, but if between years 10-20 the extinguisher requires refilling it must be tested before it can be filled.
2nd test: 10 years from 1st test
3rd & subsequent: 5 years from previous test


sorry Anthony I'm having a senior moment

are you saying that example (in bold) above is no longer in ?

Davo

  • Guest
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #4 on: October 01, 2009, 10:32:36 AM »
Mushy

BS5306:3 2009 page 5 purely says 10 year intervals
Nada else!

davo

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #5 on: October 01, 2009, 11:52:25 AM »
Thanks for the replies...it's appreciated

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #6 on: October 01, 2009, 12:20:41 PM »
Nope - just ever 10 years no with no requirement for extended services at the intervening 5 year intervals.


Much simpler than what it used to be.....

1st test 10 years from new - unless there is a continuous service history in which case it may be extended to 20 years, but if between years 10-20 the extinguisher requires refilling it must be tested before it can be filled.
2nd test: 10 years from 1st test
3rd & subsequent: 5 years from previous test


sorry Anthony I'm having a senior moment

are you saying that example (in bold) above is no longer in ?

Yes - the bold is old, not in use.

Current requirements - hydraulic test every 10 years for all cylinders including fixed systems - this is because the testing is a requirement of the various cylinder BS to meet Pressure Safety legislation & not just peculiar to portables
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #7 on: October 01, 2009, 01:18:37 PM »
Cheers Anthony - next question,Does this then apply to halon replacement and other inert gas systems?

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #8 on: October 01, 2009, 05:10:54 PM »
If they are high pressure cylinders yes. An easy way to tell is if the neck has stampings on it with the standard, weights, testing house, etc - if so, it's high pressure and subject to retesting.

Clean agent portables go through the same 10 year overhaul, but without the hydraulic test as they are low pressure.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #9 on: October 10, 2009, 08:07:52 PM »
If they are high pressure cylinders yes. An easy way to tell is if the neck has stampings on it with the standard, weights, testing house, etc - if so, it's high pressure and subject to retesting.

Clean agent portables go through the same 10 year overhaul, but without the hydraulic test as they are low pressure.
I'm no longer in the portables game, but just out of interest what are the PED pressure limit requirements ie. low/high definition? Thanks  ;)
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Hydraulic Testing of CO2 Extinguishers
« Reply #10 on: October 12, 2009, 12:31:24 AM »
I working away for a week so won't be able to look this up for a bit - if anyone else answers in the meantime it would be appreciated.

Certainly the operating pressures of water/foam/powder/wetchem which range from 8 to 18 bar appear not to require retesting in normal circumstances, although according to TG/Chubb (the only people that refurb non CO2 in any appreciable amount these days) they have to re-test any of these types if refurbished..
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36