19.7 > 18 so I would say it is over 18m high, therefore make it 90mins as stipulated.
There is good reasoning behind the increase in FR at 18m. The same reason firefighting shafts are provided. A fire would be predominantly fought from inside the building, (As the standard 135 ladder will not be of any use) the 90 mins is really to protect firefighters who will be inside the building. Also bear in mind that the presence of a FF shaft means that there is often more of a delay in the crews setting up, so it could easily be 30-40 minutes from the time of the call until the crews are in place and ready to start squirting some water. 20-30mins is not much time for dealing with the fire, performing searches, damping down etc.
If a sprinkler system is provided (Or a SHEVS) then you can quite reasonably go down the time equivalency route. It is an area of engineering not many people go near for some reason. (I think it is because it looking at heat transfer and it is not easy, and not much work has been done on measuring the actual cooling effect that a sprinkler spray has on a fire) What you are basically trying to prove is, for instance; With a sprinkler system provided (life safety would be necessary) and just 60min worth of protection the structure would react to fire no worse than if there was no sprinkler system and 90mins protection.
Also remember that similar to doors, the 90 mins is not something that will stay up for 90 minutes and falls down, it is something that survives the BS476 test for 90 minutes.