The section you are looking for is in HTM 05-03 Pt B as mentioned above.
Below is the relevant Para 4.6 & 4.7
4.6 A Category L2 or L3 system should be provided for healthcare premises other than hospitals.
A category L1 system should be provided throughout all parts of hospital premises.
However, detectors need not normally be provided in the following areas:
voids and roof spaces of any depth which contain only:
(i) MICC or wiring clipped to a metal tray or within metal conduit or trunking;
(ii) non-combustible pipework and ducts;
(iii) metal or plastic pipes used for water supply or drainage;
bath/shower rooms;
toilets in staff areas;
small cupboards (less than 1 m2);
operating theatres.
In any case the omission of detectors should be subject to a risk assessment.
4.7 Detectors should only be omitted from other areas on the basis of an assessment of fire risk.
However, the following areas should always be protected:
all patient access areas;
fire hazard rooms and areas;
rooms or departments below patient access
areas from which fire can spread vertically to
affect patient access areas;
hazard departments;
stairways, lobbies, and corridors used as means of escape where not in frequent use;
patient hotels;
commercial enterprises;
atria;
mechanical and electrical services plantrooms
(other than water tank rooms);
toilets intended for use by the public.
4.8 Omission of detectors from any area should be the
subject of consultation (see paragraph 1.16).
Para 1.16 states who the consultations should be with.
You should note the last line in para 4.7 as this is new for HTM 05-03 PT B