Author Topic: retrofitting of sypholes to fire doors  (Read 11479 times)

Offline ps

  • Jr. Member
  • **
  • Posts: 88
retrofitting of sypholes to fire doors
« on: November 12, 2009, 08:26:01 AM »
Hi all - if youve seen this post before - its because I put it on the wrong forum - so apologies for that!

Does anyone know if its acceptable to retrofit spyholes to fire doors? And, if its allowed,does anyone know a good company that could do it? The doors are fitted to students rooms in a managed block.

Many thanks in advance for any help...

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: retrofitting of sypholes to fire doors
« Reply #1 on: November 12, 2009, 08:53:29 AM »
Theres a correct answer and a practical answer.
The correct answer is that as these things drill all the way through the door they create a weakness the effect of which is impossible to predict and so the whole assembly should be subject to test.

On the other hand you have conflicting hazards of personal assault and fire safety perhaps it would be reasonable to balance thise risks by using a  steel or brass viewer, drill with care to ensure the exact fit without any gaps, and use intumescent paste around the viewer to pack the hole.

I suggest any dcent joiner should be able to do this provided the RP applies a good level of instruction and supervision
 

Offline ps

  • Jr. Member
  • **
  • Posts: 88
Re: retrofitting of sypholes to fire doors
« Reply #2 on: November 12, 2009, 08:57:18 AM »
Thanks so much Kurnal!

 The building seems otherwise to be managed well, has an alarm fitted, smoke detectors in rooms and in common areas, etc, so I think I'll go down the decent joiner route.


Davo

  • Guest
Re: retrofitting of sypholes to fire doors
« Reply #3 on: November 12, 2009, 09:08:15 AM »
ps

from memory Envirograph have this kit, saves scratting about
you can download the leaflet

davo

Offline ps

  • Jr. Member
  • **
  • Posts: 88
Re: retrofitting of sypholes to fire doors
« Reply #4 on: November 12, 2009, 09:15:09 AM »
thanks Davo!

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: retrofitting of sypholes to fire doors
« Reply #5 on: January 07, 2014, 07:58:01 PM »
Kurnal can I use your response to ps to a similar enquiry I have received, it reflects my feelings far more eloquently than I could pen.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: retrofitting of sypholes to fire doors
« Reply #6 on: January 07, 2014, 10:26:49 PM »
Tom what the eye does nae see the heart will nae grieve oer.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: retrofitting of sypholes to fire doors
« Reply #7 on: January 08, 2014, 12:01:08 PM »
Thanks Al.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: retrofitting of sypholes to fire doors
« Reply #8 on: January 09, 2014, 07:18:05 PM »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: retrofitting of sypholes to fire doors
« Reply #9 on: January 13, 2014, 10:29:07 PM »
Even if I fitted one with my new JCB drill following the instructions could I make such a c**k up that I would put somebody at risk?

Just a thought!