Fire Alarm containment
« on: November 12, 2009, 05:21:12 PM »
Can fire alarm cables (extra low voltage) and PA system cables (low voltage) be run on the same traywork without seperation?

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Fire Alarm containment
« Reply #1 on: November 12, 2009, 06:50:42 PM »
BS 5839 pt 1 26.2 l

"To avoid electromagnetic interference wth fire alarm signals, any recommendation by the manufacturer of the fire alarm equipment in respect of the seperation of fire alarm cables from the cables of other services shold be followed".

Ask the manufacturer of the cable!
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Fire Alarm containment
« Reply #2 on: November 12, 2009, 11:19:12 PM »
MICC would not be a problem , soft skinned another story , as per Mikes post.
Its time to make a counter attack !