Author Topic: Fire alarm servicing frequency  (Read 9799 times)

Offline Sherpa

  • Newbie
  • *
  • Posts: 41
Fire alarm servicing frequency
« on: November 13, 2009, 01:23:54 PM »
If you have a fire alarm that had remote transmission of fault and fire signals to a central monitoring station, and it comprised of only manual callpoints, surely you do not have to visit it twice a year. I would have thought an annual visit would be more than adequate.

The circuits are fully monitored and any fault remotley transmitted, so is two visits a year really necessary?  ::)

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Fire alarm servicing frequency
« Reply #1 on: November 13, 2009, 02:14:07 PM »
In reference to your annual visit (and here we go ) you still need a further visit to check standby batteries , so there is a clause on the annual visit so if you are not getting this I would ask questions.
So you need another visit anyway so thats why most companies on a system you descrbe would do 50% testing, ergo 2 visits. :o
Its time to make a counter attack !

Offline Sherpa

  • Newbie
  • *
  • Posts: 41
Re: Fire alarm servicing frequency
« Reply #2 on: November 13, 2009, 02:27:49 PM »
If the system is relatively simple ie only 10 manual callpoints and had 4 bells, would you still need to visit it twice a year?
« Last Edit: November 13, 2009, 02:40:54 PM by Sherpa »

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Fire alarm servicing frequency
« Reply #3 on: November 13, 2009, 02:53:48 PM »
Yes , same principle applies , read my post again .
Its time to make a counter attack !

Offline Sherpa

  • Newbie
  • *
  • Posts: 41
Re: Fire alarm servicing frequency
« Reply #4 on: November 13, 2009, 03:04:12 PM »
Thanks Galeon for your help,

I thought that with fully monitored circuits and battery presence monitoring, the service frequency could be changed to annual for relatively simple manual systems.

 ::)

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Fire alarm servicing frequency
« Reply #5 on: November 13, 2009, 05:38:10 PM »
Thanks Galeon for your help,

I thought that with fully monitored circuits and battery presence monitoring, the service frequency could be changed to annual for relatively simple manual systems.

 ::)
Period between visits should not exceed 6 months - thats what it says if you want your maintenance/service visits to comply to the current standard.
As addressable systems fully monitor all field devices (if everthing loop powered) then why not annual for them as well?