Author Topic: Auto closing doors-smoke detector distances  (Read 11076 times)

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Auto closing doors-smoke detector distances
« on: February 05, 2010, 10:22:32 AM »
Hi all

can anyone remind this auld git of the distances auto detection should be either side of an automatically closing doors. I thought it was about 18 inches...has this been changed to 7.5 metres?!

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Auto closing doors-smoke detector distances
« Reply #1 on: February 05, 2010, 10:39:11 AM »
Hi all

can anyone remind this auld git of the distances auto detection should be either side of an automatically closing doors. I thought it was about 18 inches...has this been changed to 7.5 metres?!
BS7273 Pt4 Section 13. Normally 0.5 - 1.5 but with some conditions.
We're not Brazil we're Northern Ireland.

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #2 on: February 05, 2010, 10:42:28 AM »
I don't know why I said 18 inches when I meant 1.5 metres!...I am getting old...thanks nearly there

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #3 on: February 05, 2010, 11:07:57 AM »

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #4 on: February 05, 2010, 11:16:19 AM »

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #5 on: February 05, 2010, 11:39:10 AM »
Can anyone paste on here BS 7273 part 4 Section 13...the company installing the system is saying that they can be 7.5 metres from the doors

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Auto closing doors-smoke detector distances
« Reply #6 on: February 05, 2010, 12:11:46 PM »
Mushy

for info, its six pages long with diagrams, suggest you get a copy, its very useful

13.2.4.b appears to be what you want, confirms nearlythere!


davo

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Auto closing doors-smoke detector distances
« Reply #7 on: February 05, 2010, 01:08:56 PM »
Can anyone paste on here BS 7273 part 4 Section 13...the company installing the system is saying that they can be 7.5 metres from the doors
Mushy
I'm sure you are aware that 7.5M is a number associated with the distance of the detector from any point in a room for life protection. There is no such number specified for the positioning of detection for automatic door closers.
We're not Brazil we're Northern Ireland.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Auto closing doors-smoke detector distances
« Reply #8 on: February 05, 2010, 02:49:10 PM »
There are two standard relating to auto closing doors

BS 7273-4:2007 - Code of practice for the operation of fire protection measures. Actuation of release mechanisms for doors and the Euro standard BS EN 1155:1997 Building hardware. Electrically powered hold-open devices for swing doors. Requirements and test methods
maybe you should check out both and the Euro one could be easier to understand.

« Last Edit: February 05, 2010, 02:50:42 PM by twsutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #9 on: February 05, 2010, 04:02:41 PM »
nearlythere...yes I am aware of that...and when I told the lad that this is where he was probably getting confused...he wondered off muttering summink  :)

anyhow what a day...snapped the ligaments in my finger by tucking my shirt in me trousers so its now at 90 degrees...only I could do that!  :-[

cheers davo/tw

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Auto closing doors-smoke detector distances
« Reply #10 on: February 05, 2010, 04:28:27 PM »
nearlythere...yes I am aware of that...and when I told the lad that this is where he was probably getting confused...he wondered off muttering summink  :)

anyhow what a day...snapped the ligaments in my finger by tucking my shirt in me trousers so its now at 90 degrees...only I could do that!  :-[

cheers davo/tw
Now there's a cue for a list of suggestions on what the summink was the lad was muttering.
How's about "That Mushy git has caught me out. I won't make much on this job"

As to how you bent your fingers with your hand pushed down your trousers does not bear thinking about. Cat, any suggestions?

We're not Brazil we're Northern Ireland.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Auto closing doors-smoke detector distances
« Reply #11 on: February 05, 2010, 05:01:12 PM »
The other point to make is that if detection is already in situ then the distances do not matter.  It is only where there is no detection that the distances for detection to the doors themselves have to be incorporated.

Hope the finger gets better soon, otherwise you will not be able to put it down your trousers again without someone thinking it strange.

Offline Mushy

  • Sr. Member
  • ****
  • Posts: 311
Re: Auto closing doors-smoke detector distances
« Reply #12 on: February 08, 2010, 08:39:06 AM »
well jokar you defo got me on that one...I didn't know that...so the smoke detector that is about 7 metres away from proposed new doors will suffice...I may now have a red face :(

oh the finger is now splinted up...you would have thought the simple act of tucking yer shirt into yer trousers would be straight forward enough and shouldn't really result in a trip to A&E and then the X-ray department...sorry I digress

Offline Cat

  • Full Member
  • ***
  • Posts: 248
  • I can't wait to drive with flishy flashy woo woo's
Re: Auto closing doors-smoke detector distances
« Reply #13 on: February 08, 2010, 09:07:03 AM »
Now there's a cue for a list of suggestions on what the summink was the lad was muttering.
How's about "That Mushy git has caught me out. I won't make much on this job"

As to how you bent your fingers with your hand pushed down your trousers does not bear thinking about. Cat, any suggestions?

I don't think I want to elaborate on that one.  To be safe, no comment.  On a serious note I hope your finger gets better soon.

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Re: Auto closing doors-smoke detector distances
« Reply #14 on: February 09, 2010, 08:28:13 AM »
Jokar, if the system is already in place - it don't necessarily mean it's it's been done right. Still worth pointing out to RP.