Hi,  We have a site with a 2 loop panel with 54 devices on one loop and 64 on the other, they are a mixture of Hochiki MCP, Heat, Smoke, Sounders and Beacons all on the Loop, there are 61 Beacons.
Previously there was a Kentec panel fitted which was very difficult to control, i.e. One man test would not work and it was difficult to cancel the sounders.  The Kentec was replaced by a C-Tec XFP and exactly the same thing is happening.  To get the sounders to stop the panel has to be reset about 3 times and omt does not work, there is a situation when the sounders stop and the beacons carry on flashing.
The panel seems to work fine with the sounders disabled and it always goes into fire when tested.

The installation is not ideal because the loops have been taken to a nearby box and back to the panel with 5 radials on one loop and 4 on the other, obviously a conventional system converted to addressable (not very well)!  The wiring is micc.

I spoke to C-Tec and Kentec and they seem to think the radials would make no difference to operation, I'm not so sure,  any ideas?

Thanks in advance
Cheers
Bibbage

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Addressable Problem any ideas?
« Reply #1 on: February 05, 2010, 03:14:59 PM »
I don't think the radials would be a problem. I'm guessing there are adequate short circuit isolators for each leg?

Personally I would never have gone from Kentec to C-Tec but ...

I've never had problems with Kentec/ESP one man testing and the like... we've got a few sites with networked panels and it works fine.

Is it a single stage system - are the sounders set to default ring or are they being controlled through cause and effects - are there any delays set up?
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Addressable Problem any ideas?
« Reply #2 on: February 05, 2010, 03:19:42 PM »
I would try and singular address the alarm devices , as they sit 127 behind any device they are attached to . Try this on one loop and dump the other loop out of the panel .
When you address them keep them in rotation ie 1-30 etc.
I know this is a pain to do , but to have 2 panels do the same thing is very weird.
The only thing about the wiring I can think of is maybe on the mineral , you are getting capacitance , so try loading the loop with a resistor 4k7 and see if that calms it down, check you have no earth faults, it will take a period of time for all the loop to silence as the command from the panel has to get to each device , refer to what I said above about the addresses .
Kentec should be bullet proof with Hochiki .
Best of British.
Its time to make a counter attack !

Offline bibbage

  • Newbie
  • *
  • Posts: 24
Re: Addressable Problem any ideas?
« Reply #3 on: February 05, 2010, 03:34:26 PM »
There are no delays set and no special cause and effect.

Galeon, do you mean address the sounders and the beacons separately, not sure what you mean.

Cheers
Cheers
Bibbage

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Addressable Problem any ideas?
« Reply #4 on: February 05, 2010, 03:45:24 PM »
As far as I remember OMT works for conventional bits; it disables the conventional outputs of a radial output circuits, but has no effect on loop powered outputs, which have to be isolated by program... etc. or am I wrong?
« Last Edit: February 05, 2010, 09:01:04 PM by Benzerari »

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Addressable Problem any ideas?
« Reply #5 on: February 05, 2010, 05:03:40 PM »
Could be the possibility of too much current draw in alarm???  Kentec and C-TEC panels don't have a particularly high loop current output, causing the issue of not many alarm devices being able to oeprate on a single loop. 
** Knowledge is power, I'm still working on both **

Offline bibbage

  • Newbie
  • *
  • Posts: 24
Re: Addressable Problem any ideas?
« Reply #6 on: February 05, 2010, 05:21:30 PM »
Hi Big Fella,  I checked loop voltage in alarm and it was not much lower than in normal state.
Cheers
Bibbage

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Addressable Problem any ideas?
« Reply #7 on: February 05, 2010, 07:02:26 PM »
There are no delays set and no special cause and effect.

Galeon, do you mean address the sounders and the beacons separately, not sure what you mean.

Cheers

Yep
Its time to make a counter attack !

Graeme

  • Guest
Re: Addressable Problem any ideas?
« Reply #8 on: February 06, 2010, 08:14:47 PM »
Hi,  We have a site with a 2 loop panel with 54 devices on one loop and 64 on the other, they are a mixture of Hochiki MCP, Heat, Smoke, Sounders and Beacons all on the Loop, there are 61 Beacons.
Previously there was a Kentec panel fitted which was very difficult to control, i.e. One man test would not work and it was difficult to cancel the sounders.  The Kentec was replaced by a C-Tec XFP and exactly the same thing is happening.  To get the sounders to stop the panel has to be reset about 3 times and omt does not work, there is a situation when the sounders stop and the beacons carry on flashing.
The panel seems to work fine with the sounders disabled and it always goes into fire when tested.

The installation is not ideal because the loops have been taken to a nearby box and back to the panel with 5 radials on one loop and 4 on the other, obviously a conventional system converted to addressable (not very well)!  The wiring is micc.

I spoke to C-Tec and Kentec and they seem to think the radials would make no difference to operation, I'm not so sure,  any ideas?

have experienced a delay in pressing the silence button to the last sounder stopping.
i know with other panels that beacons that are programmed as other outputs they will not stop when sounders silence is pressed-only reset.

you will have more capacitance on the loop in micc and it also reduces your loop lengths. check for earth faults etc

Thanks in advance

Offline bibbage

  • Newbie
  • *
  • Posts: 24
Re: Addressable Problem any ideas?
« Reply #9 on: February 07, 2010, 09:46:40 AM »
There is the usual delay when silencing, but I can hear sounders faintly from furthest area away from panel and then they gradually get closer until they are all sounding again, as I said I have to reset about 3 times to get them to stop.

I will try loading the loops with a resistor to counter act any capacitance, easiest option!

As for earth faults, because the radials are terminated in a plastic box adjacent to the panel the earths are not connected, there are no earth faults at the connection box.  Perhaps another thing to try connecting them up to the panel!
Cheers
Bibbage

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Addressable Problem any ideas?
« Reply #10 on: February 08, 2010, 03:46:25 AM »
It might be worth hanging another panel off the loops , maybe a cel , they work well with Hochiki , just a thought.
Its time to make a counter attack !

Graeme

  • Guest
Re: Addressable Problem any ideas?
« Reply #11 on: February 10, 2010, 09:32:59 PM »
I had an Aritech panel that the sounders took ages to silence and eventually would not silence and the reset button would have to be pressed.

We replaced for an Advanced Panel and this cured the problem . the sounders stop almost instantly now.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Addressable Problem any ideas?
« Reply #12 on: February 11, 2010, 09:06:31 AM »
I agree that the most likely cause of the problem is the capacitance caused by using MICC cables. This can seriously affect the data signals on an addressable system. In this case, the data signal being sent to switch off devices, is being corrupted by the effect of the capacitance and some/all are not responding to it

The situation with the radials is not the problem, and as long as one radial doesn't cover any area greater than 2000m2 then it also complies with BS.


Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Addressable Problem any ideas?
« Reply #13 on: February 11, 2010, 08:21:49 PM »
Do you have the same problem if you stick 0 volts on the "continuous" input ?
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline bibbage

  • Newbie
  • *
  • Posts: 24
Re: Addressable Problem any ideas?
« Reply #14 on: February 11, 2010, 10:38:57 PM »
If capacitance is the most likely cause and I tend to agree, will loading the loop with resistance reduce it's effect?  Will the capacitance be greater because of the radial circuits, in other words would there still be a problem if was a true loop?
Thanks for all the replies so far.
Do you have the same problem if you stick 0 volts on the "continuous" input ?  not sure what you mean by this David.