The Factory Mutual guidance does not like automatic vents with sprinkler systems:
“2.1.1.10 Heat and Smoke Venting
2.1.1.10.1 Factory Mutual Research recommended protection is based on roof vents and draft curtains not being provided. Fire tests have not shown automatic vents to be cost-effective, and they may even increase sprinkler water demand. Hence, permanent heat and smoke vents, if installed, should be arranged for manual operation or equipped with fusible links rated at a minimum 360°F (182°C). Smoke removal during mop-up operations can frequently be achieved through eave-line windows, doors, monitors, nonautomatic exhaust systems (gravity or mechanical) or manually operated heat and smoke vents.”
But, as you say, other guidance does not have a problem with it, and the guidance supporting the Greater Manchester Act states the 'experiments have shown...' qoute in the original post. It does, however state that vents should not be automatic if ESFR system is to be used, and this is also stated in the SVA Guide.