Just to confirm what has gone ahead.
We are primarily interested in the early fire growth rate and its potential to inhibit means of escape.
If the chairs are laid out in rows in the hall, how significant is their contribution going to be to the initial growth of a fire that starts in material around or beneath them? Not very, I would suggest. Firstly, the fire loading presented by the chairs is very spread out and secondly, even if one or two chairs do become involved in the fire early in its development, this is not likely to occur before all the occupants have left the hall - assuming exits are ok [the more people in the hall, the earlier the fire will be spotted].
If the chairs are stacked within the hall then they present a much more significant fire loading. But, even so, are they likely to be a major contributor to the fire growth during the evacuation stage? The fire will be noticed early, again, and if the exits are adequate then people will be able to evacuate in good time before the chairs start to contribute to fire development.
Care and judgement may be required in both the above cases, as there are often inner rooms or upper levels where people may be and which have questionable means for giving early warning of fire as well as means of escape that may rely on the main hall remaining tenable.
If the chairs are stacked in a separate room to where all the people are (a store or back room) then the fire may have time to develop to a stage where the chairs contribute significantly to the fire growth before the fire becomes noticed. But in this case the chairs are in a separate space and the means of escape for the occupants of the hall should be safe for sufficient time to evacuate.
If BLEVE's figure of 2000kW is right for 5 or 6 chairs then a hundred or so chairs is quite a fire load! There could ultimately be a lot of damage to the property due to the fire loading.
As for fixing the chairs, this is usually advisable. You do not want people ploughing through the lines of chairs to get to the exits, you want people to follow the rows so that everyone has the best routes to the exits. A factor that can affect the need for interlinking the chairs is the provision of normal and emergency lighting. If the audience may be plunged into darkness or semi-darkness then the need for interlinking of chairs is greater. If there will always be bags of light available then the need for interlinking diminishes.
Finally, Cullenloon, are you in Cullen? I am.
Stu