Author Topic: Shops and retail outlets  (Read 4966 times)

Offline stugood

  • Newbie
  • *
  • Posts: 3
Shops and retail outlets
« on: September 07, 2010, 04:30:51 PM »
When does a shop/retail warehouse over 2000 square metres not require compartmentation and/or sprinklers??

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Shops and retail outlets
« Reply #1 on: September 07, 2010, 11:21:41 PM »
If it is existing and has not been substantially altered or subject to a change of use for many years. The standard solution in the curent ADB is to limit compartment size or install sprinklers to limit the size of a fire and reduce risk to environment and fire fighters.  But this has not always been the case.
And of course the Building Regualtions are only applied on erection, alteration or material change of use.
In some cases fire and building authorities have accepted extensions to existing unsprinklered shops because it seemed excessive to require a full installation in an existing unsprinklered building just becasue of a relatively small extension taking it over 2000 sq m. In other cases other engineered solutions may have been found.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Shops and retail outlets
« Reply #2 on: September 07, 2010, 11:52:17 PM »
When was it built and is it single storey because it appears at one time compartmentation was not required in single storey buildings? (1965 Building Regs)
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Shops and retail outlets
« Reply #3 on: September 09, 2010, 12:04:33 PM »
When does a shop/retail warehouse over 2000 square metres not require compartmentation and/or sprinklers??

When it's a warehouse.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Shops and retail outlets
« Reply #4 on: September 12, 2010, 10:02:11 PM »
Just off the top of my head, so correct me if I'm wrong, the size limit given in ADB changed in the 2000 iteration of the document from 4000 sq m to 2000 sq m, so if it was built before the year 2000 and is below 4000 sq m then it may well not have sprinklers.

Stu