Thanks Stu. Yes I took that at its face value- acrylic fibre yarn and other materials that are not easily extinguished by sprinklers.
If you compare it with a shop, in which single and double rails of clothing can be tightly packed in to a shop floor and may be covered by OH sprinklers delivering just 5mm/sqm/min then three rows is not all that much worse. And boy these are big - K360 heads as opposed to the K80 in a typical shop. Probably 25mm/sqm/min? So it seems a bit extreme to say no you cant put three rows in.
I see the big problem being the potential rapid lateral spread of the fire to affect more sprinklers than the water infrastructure can support, unless we do something to limit the potential area affected by fire.
Under ESFR sprinklers I could stack for example exposed foam rubber to a height of 7.6m with K200 heads, thats easy because this appears in the table.
Both the FM and TB209 are very clear that ESFR must only be used to cover risks for which tests have been carried out. It seems no tests have been carried out on hanging garments and ESFR. So we cant do it.
But I cant tell a fashion chain to stop selling clothes and it would be crackers tell them to take out the sprinklers or downgrade them just because because hanging garments dont appear on the tables!