A new hotel, with bedrooms covering three floors leading into communal corridors and one single stair well. Installed is an L1 fire alarm system with immediate evacuation to BS 5839-1:2002+A2:2008
BS 9999:2008 states in 33.4.5.1
“Smoke detector operated fire/smoke dampers should be installed in all occupancy characteristic Cii and Ciii buildings, unless all occupants of the building can be expected to make an unaided escape and an L1 fire alarm system is installed in accordance with the recommendations given in BS 5839-1:2002+A2:2008, in which case the following exceptions may be made.
a) If the alarm system is arranged so that on the detection of smoke it signals the immediate evacuation of all the occupants of the building, then fire/smoke dampers are not needed.”
Consultants are arguing that they are needed. I would welcome any comments