Author Topic: Automatic Hold Open Devices  (Read 13013 times)

Offline Stinky

  • Newbie
  • *
  • Posts: 35
Automatic Hold Open Devices
« on: October 14, 2010, 07:00:24 PM »
What is everyone's opinion on automatic hold open devices to the majority of fire doors in a property with only a manual fire alarm system?

I personally don't like it.  I would prefer to see no hold open devices or an automatic detection system.

Or am I being a bit over the top?

Would management suffice i.e. anyone leaving the building WILL hit a break glass call point?

Stinky

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Automatic Hold Open Devices
« Reply #1 on: October 14, 2010, 08:32:05 PM »
I suggest you read "BS 7273-4:2007 Code of practice for the operation of fire protection measures – Part 4: Actuation of release mechanisms for doors".  This gives, amongst other advice, guidance about detector locations relative to such devices.

Stu


Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Automatic Hold Open Devices
« Reply #2 on: October 14, 2010, 09:19:12 PM »
What is everyone's opinion on automatic hold open devices to the majority of fire doors in a property with only a manual fire alarm system?

I personally don't like it.  I would prefer to see no hold open devices or an automatic detection system.

Or am I being a bit over the top?

Would management suffice i.e. anyone leaving the building WILL hit a break glass call point?

Stinky
A hold open device without a detection system is like an extinguisher without the water.
We're not Brazil we're Northern Ireland.

Offline Stinky

  • Newbie
  • *
  • Posts: 35
Re: Automatic Hold Open Devices
« Reply #3 on: October 14, 2010, 09:35:35 PM »
I suggest you read "BS 7273-4:2007 Code of practice for the operation of fire protection measures – Part 4: Actuation of release mechanisms for doors".  This gives, amongst other advice, guidance about detector locations relative to such devices.

Stu



We wouldn't have a forum for questions if we all read the guides ;)

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Automatic Hold Open Devices
« Reply #4 on: October 14, 2010, 10:52:31 PM »
I suggest you read "BS 7273-4:2007 Code of practice for the operation of fire protection measures – Part 4: Actuation of release mechanisms for doors".  This gives, amongst other advice, guidance about detector locations relative to such devices.

Stu



We wouldn't have a forum for questions if we all read the guides ;)

Equally it's a bit difficult to provide comprehensive answers if you haven't read the guides !!

7273 pt 4 section 13 suggests category L1/L2/or L3 as suitable (without further modification) for buildings with hold open devices.

Alternatively an L5 system can be specified requiring careful planning and positioning of detectors near to doors utilising the hold open devices.

In short, hold open devices in a building with no automatic smoke detection doesn't comply with 7273 pt 4 and although I'm no risk assessor it sounds to me like they should be disconnected until properly assessed and automatic detection installed.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Automatic Hold Open Devices
« Reply #5 on: October 15, 2010, 07:17:53 AM »
...... and a cracking wee standard it is too.  Why would anyone giving professional advice not already have a copy?

I had a colonoscopy and ogd this week ( I just love the drugs they give you for the procedure).  I am going to check medicnet, cos I bet I will find that the prof who did the procedure has a question telling people what he found and asking them what advice he should give me when I go for the follow up appointment. If I find it and read it, I will certainly cancel my appointment and save myself the fee, though I do like the nurses who bring me the coffee.
Colin Todd, C S Todd & Associates

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Automatic Hold Open Devices
« Reply #6 on: October 15, 2010, 09:07:23 AM »
CT

Hope all is well and you're not mincing around too much ::)


davo

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Automatic Hold Open Devices
« Reply #7 on: October 15, 2010, 09:39:42 AM »
...... and a cracking wee standard it is too.  ............

Don't get me started again  ;)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Automatic Hold Open Devices
« Reply #8 on: October 15, 2010, 10:24:42 AM »
Stinky you haven't said what type of automatic hold open devices you are referring to, electrical, acoustic or wireless operated and is there location acceptable according to your FRA?
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Automatic Hold Open Devices
« Reply #9 on: October 15, 2010, 01:12:47 PM »
Just to throw a thought in here:

If the premises is truly suitable for a manual fire alarm system, i.e. People would sound the alarm and a fire would not be able to grow unnoticed, then maybe it is not as much of a problem as we are making out.


Offline FSO

  • Full Member
  • ***
  • Posts: 216
Re: Automatic Hold Open Devices
« Reply #10 on: October 15, 2010, 01:23:15 PM »
Totally agree Civvy.

After all, isn't that the whole point of a Fire risk assessment?

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Automatic Hold Open Devices
« Reply #11 on: October 15, 2010, 01:42:15 PM »
Just to throw a thought in here:

If the premises is truly suitable for a manual fire alarm system, i.e. People would sound the alarm and a fire would not be able to grow unnoticed, then maybe it is not as much of a problem as we are making out.



I agree with you obviously  like minded people will also , but I have numerous occasions where persons are adverse to using call points , unless they want to get out of Bescos with their shopping without paying............... wouldn’t dream of it myself always use a test key more professional  ;D
Its time to make a counter attack !

Offline Tom W

  • Hero Member
  • *****
  • Posts: 603
Re: Automatic Hold Open Devices
« Reply #12 on: October 15, 2010, 02:09:23 PM »
...... and a cracking wee standard it is too.  ............

Don't get me started again  ;)

prod  ;)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Automatic Hold Open Devices
« Reply #13 on: October 15, 2010, 02:22:29 PM »

If the premises is truly suitable for a manual fire alarm system, i.e. People would sound the alarm and a fire would not be able to grow unnoticed, then maybe it is not as much of a problem as we are making out.

Thats fine providing you are prepared to treat the appropriate British standards as recommendations and ignore them. Then there's that man with the curly wig and can you put a good enough case to him if required.
« Last Edit: October 15, 2010, 02:24:13 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline FSO

  • Full Member
  • ***
  • Posts: 216
Re: Automatic Hold Open Devices
« Reply #14 on: October 15, 2010, 02:46:35 PM »

If the premises is truly suitable for a manual fire alarm system, i.e. People would sound the alarm and a fire would not be able to grow unnoticed, then maybe it is not as much of a problem as we are making out.

Thats fine providing you are prepared to treat the appropriate British standards as recommendations and ignore them. Then there's that man with the curly wig and can you put a good enough case to him if required.

Ahem!       http://fire.org.uk/forum/index.php?topic=4952.0 ;)
« Last Edit: October 15, 2010, 02:48:22 PM by FSO »