Author Topic: fire alarm containment  (Read 10607 times)

Offline Sherpa

  • Newbie
  • *
  • Posts: 41
fire alarm containment
« on: October 20, 2010, 05:35:24 PM »
Gents

Am i correct in saying that under BS5839 A2 you can install fire alarm cables in pyro along side PA cables in FP200?....When i say along side they are to installed on the same traywork..

I always thought they could not be mixed, but now am been told otherwise.

thanks

Sherpa

Graeme

  • Guest
Re: fire alarm containment
« Reply #1 on: October 21, 2010, 06:35:11 PM »
MICC cable has it's own mechanical protection and is not likely to be damaged by other cables being installed in the same tray.
Not seen that part in A2 but that's not to say it there. Most jobs i have been on now have one tray for all ELV cables to be installed on.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: fire alarm containment
« Reply #2 on: October 23, 2010, 04:36:32 PM »
To do what you say is fine with the only proviso that neither manufacturer says you shouldn't (for EMC reasons).
Colin Todd, C S Todd & Associates

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: fire alarm containment
« Reply #3 on: October 27, 2010, 06:07:20 PM »
Selv ?
Its time to make a counter attack !

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: fire alarm containment
« Reply #4 on: October 28, 2010, 08:47:07 AM »
dont be so old fashioned Pauley. But talking of SELV, I am having a birthday bash on 6 November, would you yourSELV like to come>
Colin Todd, C S Todd & Associates

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: fire alarm containment
« Reply #5 on: October 28, 2010, 11:00:37 AM »
Well Colin that would be lovely as it appears our birthdays fall on the same day  ;D
Its time to make a counter attack !

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: fire alarm containment
« Reply #6 on: October 29, 2010, 07:03:30 AM »
Farnham Castle at around 8pm.  Have hired a soul band (on the proviso they do as many rock songs as they know!). Be there or be square.