Author Topic: Pub with living accommodation above  (Read 29378 times)

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Pub with living accommodation above
« Reply #15 on: December 07, 2010, 11:00:28 AM »
Good point, NT.

I was consulted once on a sheltered housing (termed 'very sheltered housing' - their phrase) development where "jumpy outy" windows were proposed for the first floor bedrooms because the bedrooms were inner to the living room and kitchen.  They complied with ADB stipulations and I was powerless to influence the design.  There were many of these flats and I am sure there is a good probability that the design will result in at least one death during the lifetime of the building, it will only take one resident to leave something on the cooker and then nod off in the bedroom - the classic scenario.


Stu


Offline tmprojects

  • Sr. Member
  • ****
  • Posts: 281
Re: Pub with living accommodation above
« Reply #16 on: February 27, 2011, 01:35:45 AM »
Stu

One of your ex-colleagues did his BEng dissertation on inner-room bedrooms with sprinklers in the access room and I believe that he proved that even with sprinklers the access room would be untenable.



do you know if any similare test has been carried out, or report exists to show this? would be a very interesting read.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Pub with living accommodation above
« Reply #17 on: February 27, 2011, 04:16:03 PM »
BRE report no. 204505.  Freely available on the interwet.

Stu